View Full Version : ATO with RO/DI selonoid valve


kidney514
02/25/2008, 09:37 PM
Not that I did alot of research on this one. But what is the best way to configure that in the profilux

Selonoid valve is NC (normally closed).

And in the spirit off sharing settings that will posted for other also ;)

AQD_ottawa
02/26/2008, 05:47 AM
Have the socket function it is attached to in off state when water is at the level required, this is set in ATO setup

kidney514
02/28/2008, 06:24 PM
This has been done, and in either state teh socket doesn't turn on?

AQD_ottawa
02/28/2008, 07:02 PM
what function have you got set, it sounds like its not Auto top off, please refer to section 3.11.1 of 3.08 manual

link

http://www.ghl-kl.de/Produkte/Aquaristik/Download/Manual_ProfiLuxII_V308.pdf

kidney514
02/28/2008, 07:25 PM
Got it everything configured right except for the maximum on time was set to 1 min and created the problem, now it all good :)