View Full Version : APEX Check my program, couple of questions.


jduck
09/02/2010, 08:44 PM
SndAlm_I6
Sound B
Set OFF
If Temp > 85.0 Then ON
If Temp < 75.0 Then ON
Defer 000:30 Then ON

SndWrn_I7
Sound A
Set OFF
If Temp > 83.0 Then ON
Defer 000:30 Then ON

EmailAlm_I5
Set OFF
If Temp > 85.0 Then ON
If Temp < 75.0 Then ON
If Power EB8_3 Off 001 Then ON
If Power EB8_4 Off 001 Then ON
If Power EB8_5 Off 001 Then ON Did receive an email alert today For this but checked status online and it was on and showed Amps???
I use to have If Power Apex Off 001 Then ON but received one email an hour and discontinued it after the first day of use. Does this happen when it reloads/refreshes?
Defer 000:30 Then ON

Refuge
Fallback OFF
Set OFF
If Outlet T5_1 = OFF Then ON

UV
Fallback OFF
Set OFF
If Outlet RTN_PUMP = ON Then ON
If Temp > 81.0 Then OFF

VORTECH_1
Fallback ON
Set ON

3_4 Unused
Fallback OFF
Set OFF


3_5 Unused
Fallback OFF
Set OFF

3_6 Unused
Fallback OFF
Set OFF

3_7 Unused
Fallback OFF
Set OFF

HEAT2
Fallback OFF
Set OFF
If Temp < 77.0 Then ON
If Temp > 78.0 Then OFF
If Temp < 75.0 Then OFF

CARBON
Fallback ON
Set ON

PHOS
Fallback ON
Set ON

RTN_PUMP
Fallback ON
Set ON
If FeedA 002 Then OFF
If Outlet Auto_Feed = OFF Then OFF

ATO
Fallback OFF
Set OFF
OSC 179:30/000:30/000:00 Then ON

CaRx_circ
Fallback ON
Set ON

CaRx_pump
Fallback OFF
Set ON
If Outlet RTN_PUMP = OFF Then OFF

SKIM
Fallback ON
Set ON
If Outlet RTN_PUMP = OFF Then OFF
If FeedA 002 Then OFF

HEAT1
Fallback OFF
Set OFF
If Temp < 77.3 Then ON
If Temp > 77.0 Then OFF

T5_1
Fallback OFF
Set OFF
If Sun 120/240 Then ON
If Temp > 82.0 Then OFF
Min Time 030:00 Then OFF

T5_2
Fallback OFF
Set OFF
If Sun 240/120 Then ON
If Temp > 82.0 Then OFF
Min Time 030:00 Then OFF

Co2
Fallback OFF
If pH2 > 06.25 Then ON
If pH2 < 06.20 Then OFF
If Outlet CaRx_pump = Off then OFF



CHILL
Fallback ON
Set ON
If Temp < 75.0 Then OFF

FEED
Fallback OFF
Set OFF
If Outlet Auto_Feed2 = ON then ON
Would like to have this Turn ON 2 minutes after FeedA goes ON.

VORTECH_2
Fallback ON
Set ON

FAN
Fallback OFF
Set OFF
If Outlet T5_1 = ON then ON
Would like it to stay on additional 15 min After the lights go out?? Should I just use If Sun 120/255 Then ON?? or is there another option using another comand?


VTECH_BATT
Fallback ON
Set ON


VIRTUAL OUTLETS
I use these 2 for autofeed with superfeeder
Auto_Feed
Set ON
If Time 13:00 to 14:30 Then OFF
If Time 17:30 to 18:00 Then OFF


Auto_Feed2
Set OFF
If Time 13:01 to 13:02 Then ON
If Time 17:31 to 17:32 Then ON

Picked these out of the book and decided to try them out.
Vortech_7_1
Fallback ReefCrst
Set Pulse
If Time 08:00 to 10:00 Then ReefCrst
If Time 12:00 to 14:00 Then TidalSwl
If Time 16:00 to 17:30 Then Nutrient
If Time 23:00 to 07:00 Then Night
If FeedA 000 Then Slow
If Outlet Auto_Feed = ON Then Slow

Vortech_7_2
Set Anti-Syn
If Time 08:00 to 09:00 Then Sync
If Time 12:00 to 13:00 Then Sync
If Time 16:00 to 17:30 Then Sync
If Time 22:00 to 07:00 Then Night
If FeedA 000 Then Slow
If Outlet Auto_Feed = ON Then Slow



Would like to add a email and audible alarm for conductivity also.

swearint
09/03/2010, 08:17 AM
I use to have If Power Apex Off 001 Then ON but received one email an hour and discontinued it after the first day of use. Does this happen when it reloads/refreshes?

With the current firmware release, there are two options for Apex Power detection: via the aquabus or via the 12V adapter. So if you have it set to power adapter and no adapter is present, that could be the issue. I don't remember the exact menu sequence, so see the Unofficial Users Guide on how to set the power option.


3_4 Unused
Fallback OFF
Set OFF

3_5 Unused
Fallback OFF
Set OFF

3_6 Unused
Fallback OFF
Set OFF

3_7 Unused
Fallback OFF
Set OFF

It's not clear here, but make sure that each outlet name is unique. The Apex has problems if outlet names are duplicated.


HEAT2
Fallback OFF
Set OFF <---Not needed
If Temp < 77.0 Then ON
If Temp > 78.0 Then OFF
If Temp < 75.0 Then OFF

HEAT1
Fallback OFF
Set OFF <--- Not needed
If Temp < 77.3 Then ON
If Temp > 77.0 Then OFF

The Set OFF will interfere with your desired control band, shutting the heater off as soon as the ON condition is no longer true.


CHILL
Fallback ON
Set ON
If Temp < 75.0 Then OFF

I assume you are relying on the chiller thermostat to control with the Apex providing backup override. You would probably get finer control by letting the Apex control and relying on the thermostat as backup.


FEED
Fallback OFF
Set OFF
If Outlet Auto_Feed2 = ON then ON
Would like to have this Turn ON 2 minutes after FeedA goes ON.

You could add:
If FeedA 000 Then ON
Defer 002 Then ON

Keep in mind that the Defer applies to the whole outlet, so it would also delay on Auto_Feed2


FAN
Fallback OFF
Set OFF
If Outlet T5_1 = ON then ON
Would like it to stay on additional 15 min After the lights go out?? Should I just use If Sun 120/255 Then ON?? or is there another option using another comand?

Add:
Defer 015 Then OFF


Would like to add a email and audible alarm for conductivity also.
Simply add the appropiate probe name to each desired alarm/email outlet. I don't use the conductivity probe, but I think it would be:

If Condx < yy Then ON

Where x is the address of the PM.


Todd

aquamanic
09/03/2010, 09:50 AM
if you have it set to power adapter and no adapter is present, that could be the issue

X2

Turn it on/off via the display module: System - Misc Setup - Power Monitor