View Full Version : Leak sensor


Maives
12/02/2010, 09:38 PM
I purchased a GRI 2800 leak sensor that requires 5 VDC to activate. It is a NO switch. Am I correct to assume that I can wire this to the Apex breakout box with 5V applied or do I need a relay? The Unofficial User Guide indicates that it can handle 5V but no more.

If I need a relay, will this do?
http://www.radioshack.com/product/index.jsp?productId=2062478

kenargo
12/02/2010, 11:08 PM
It looks like the sensor you have is intended to be used on a loop that can supply a voltage (to run the sensor); that will not work connected directly to the Apex but I found a wiring diagram that shows how to inline a relay and that can be used with the Apex; just be sure to NOT connect the powered loop to the Apex; use the relay contact to connect to the Apex.

This is the diagram I found:

http://www.grisk.com/specialty/pdf/2800%20water%20sensor.pdf

Maives
12/03/2010, 12:12 AM
What do you think of the reed relay I linked to? I assume the 5V can open and close the relay and it is small enough that it can fit in my DIY breakout box.

kenargo
12/03/2010, 12:41 PM
I think it will work fine.