View Full Version : On Off Bsmsnt pump


Osama
10/19/2014, 10:38 AM
I would like to pump my pump on 5 mnts and off 55 mnts throughout the day for mixing salt in my storage tanks. Other times I would like it to be on standby till I ask it to run continuously, till I stop it. This mode for moving water from storage tank to upstairs DT. What are the commands for each function and can they both be combined in same outlet configuration.

kurt_n
10/19/2014, 10:59 PM
For the 5 minutes on, 55 minutes off every hour... the code would be something like:

Fallback OFF
Set OFF
OSC 000:00/005:00/055:00 Then ON

As far as the rest, from what you describe I'd probably just opt to turn the outlet manually "ON" when I wanted it to run continuously, then turn it back to "AUTO" to turn if off. That would be the simplest method, however I'm sure you could do it other ways using Feed Cycles, or virtual outlets.

Osama
10/20/2014, 06:56 AM
Thanks Kurt will do that Appreciate it