Unread 07/31/2009, 09:37 AM   #1
luvreefs23
Registered Member
 
Join Date: Feb 2008
Posts: 758
Electrical - Did i do this right?

I have to dedicated outlets to my new tank each on their own 20 amp circuit. Each have 3 gfci receptacles in the box. When i test the first one it trips and cuts power to that one and the 2 after it, if i trip the last one then the last one is the only one without power and if i do the middle one then that one and the one after it cuts power...sounds correct from what i understand. Im posting a couple pics just to show how its wired, i used 12-2 wire. I imagine to an electrician from what i have explained and my pictures it should be a piece of cake for someone to verify for me. Here they are:










Help is greatly appreciated.

Thanks
Dennis


luvreefs23 is offline   Reply With Quote
Unread 07/31/2009, 10:07 AM   #2
dave2184
Registered Member
 
dave2184's Avatar
 
Join Date: Jul 2003
Location: Girard, Oh.
Posts: 2,549
That'll work but, I'd split each off individuay so one failed device won't trip the whole system.


I had mine done how you have your setup now and, a failed powerhead set off all of them and caused my tank to crash do to a compleate loss of circulation.

Edit: WOW my spelling sucks today!


__________________
-Dave-

"Oh ya - I missed one important point. There are other ways to deal with phosphates like phosphate sponges, but it's kind of like trying to fan the stink off a dead skunk." -looser

Last edited by dave2184; 07/31/2009 at 10:24 AM.
dave2184 is offline   Reply With Quote
Unread 07/31/2009, 10:16 AM   #3
b_s_c1
Registered Member
 
Join Date: Apr 2009
Location: Victoria, Texas
Posts: 466
+1

You have them wired in series so if the first one trips it will take out all of the rest.

Wire them parallel so the only receptical that will trip would be the one with the problem. To do this run a power and neutral from each recptical to the home run then tie all the power wires together and all the neutral wires together.


b_s_c1 is offline   Reply With Quote
Unread 07/31/2009, 10:16 AM   #4
troylee
Moved On
 
troylee's Avatar
 
Join Date: Oct 2008
Location: here.
Posts: 2,509
You can wire them anyway you like but personally I would not want one to trip the other.....on your pig tail you need to splice the hot wire "black" into 3 ind. Wires and run one to each socket this will prevent one gfi from popping the other 2. Same with your nuetral "white" ...the grounds can be jumped from one socket to the next thou.....


troylee is offline   Reply With Quote
Unread 07/31/2009, 11:03 AM   #5
uncleof6
Registered Member
 
uncleof6's Avatar
 
Join Date: Jul 2004
Location: AWOL
Posts: 12,013
Re: Electrical - Did i do this right?

Quote:
Originally posted by luvreefs23
I have to dedicated outlets to my new tank each on their own 20 amp circuit. Each have 3 gfci receptacles in the box. When i test the first one it trips and cuts power to that one and the 2 after it, if i trip the last one then the last one is the only one without power and if i do the middle one then that one and the one after it cuts power...sounds correct from what i understand. Im posting a couple pics just to show how its wired, i used 12-2 wire. I imagine to an electrician from what i have explained and my pictures it should be a piece of cake for someone to verify for me. Here they are:










Help is greatly appreciated.

Thanks
Dennis
As stated above, you have GFCIs improperly connected to the load side of the first and second GFCI. (Right to left) You can connect NON- GFCI outlets to the load side of a GFCI, and that is how I would wire this, since you have two circuits, (half your circulation on both) Also, you have exposed conductors, both hot and neutral at the back of the GFCIs. When this is "stuffed" into the box, your grounding wires will be in close proximity to the exposed conductors, perhaps even touching. With regular outlets, this is not really an issue, as the neutral and ground are bonded in the main panel, however with a GFCI, a neutral - ground fault in the supply line will cause the GFCI to trip. This is not known to everyone, especially if they have never spent hours trying to find and fix a ground fault nuisance tripping a GFCI. I suspect this is the number one reason for nuisance tripping with DIY/Aquarium electrical, Followed by overloaded circuits and highly inductive loads.

I have arbitrarily decided to add this to all GFCI questions:

A GFCI will not protect you if you contact both the line (hot) and neutral conductors.

A GFCI will not protect you if you contact the output side of a ballast or transformer (since they isolate)

Only two examples, the list continues on.

Regards,

Jim


__________________
"Things should be made as simple as possible, but not simpler." (oft attributed to Einstein; most likely paraphrasing by Roger Sessions; compactly articulates the principle of Occam's Razor)

Current Tank Info: 325 6' wide Reef

Last edited by uncleof6; 07/31/2009 at 11:16 AM.
uncleof6 is offline   Reply With Quote
Unread 07/31/2009, 11:05 AM   #6
ilv4xn
Registered Member
 
Join Date: Aug 2008
Location: portland OR
Posts: 162
+1 for troy. that's how I would wire it


__________________
Don't force it. Get a bigger hammer!

Current Tank Info: 50gal
ilv4xn is offline   Reply With Quote
Unread 07/31/2009, 11:47 AM   #7
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
How to wire multiple GFCIs to a single branch circuit:


Now lets talk about what I see in the photos: (please take this as kind advice, as your safety is what is important here).

You have used the "stab-ins" on the backs of the receptacles and you have a good bit of bare conductor showing. Never use "stab-ins", they make a very poor connection and are very prone to working lose due to thermal expansion and contraction. ALWAYS use the screw lugs and use them properly.


I don't even like the illustration that much, as I prefer to see the conductor wraped tighter around the screw so that it can not fall off even if the screw becomes loose.

ALWAYS wrap in the same direction that the screw tightens (clockwise looking at the top of the screw for most devices).


BeanAnimal is offline   Reply With Quote
Unread 07/31/2009, 11:48 AM   #8
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by troylee
You can wire them anyway you like but personally I would not want one to trip the other.....on your pig tail you need to splice the hot wire "black" into 3 ind. Wires and run one to each socket this will prevent one gfi from popping the other 2. Same with your nuetral "white" ...the grounds can be jumped from one socket to the next thou.....
Actualy... the grounds should be pigtailed or a single continuous conductor that loops to each device.


BeanAnimal is offline   Reply With Quote
Unread 07/31/2009, 02:06 PM   #9
luvreefs23
Registered Member
 
Join Date: Feb 2008
Posts: 758
Im lost....lol


luvreefs23 is offline   Reply With Quote
Unread 07/31/2009, 02:18 PM   #10
troylee
Moved On
 
troylee's Avatar
 
Join Date: Oct 2008
Location: here.
Posts: 2,509
just take your home run and split each wire into 3 with a wire nut and 3 short wires......so you have 3 black, 3 white, and 3 green then run a single wire to each gfi......then your done....bean put it out there plain and simple if you cant see it from the digram i would recommend letting someone else wire it for ya....before you get hurt or burn the house down....


troylee is offline   Reply With Quote
Unread 07/31/2009, 02:20 PM   #11
troylee
Moved On
 
troylee's Avatar
 
Join Date: Oct 2008
Location: here.
Posts: 2,509
all you are using on the diagram is the "line "wire as you can see the load is cut off"dont use them"....


troylee is offline   Reply With Quote
Unread 07/31/2009, 02:27 PM   #12
uncleof6
Registered Member
 
uncleof6's Avatar
 
Join Date: Jul 2004
Location: AWOL
Posts: 12,013
Quote:
Originally posted by luvreefs23
Im lost....lol
Well you may be lost, but you actually have the recepticles oriented correctly. The NEC does not mention this, but the "inventor" intended the ground terminal of the recepticle to be up, rather than the common usage which is at the bottom.

Does this help?



Or if you decide against multiple GFCIs, maybe this will help:



Jim


__________________
"Things should be made as simple as possible, but not simpler." (oft attributed to Einstein; most likely paraphrasing by Roger Sessions; compactly articulates the principle of Occam's Razor)

Current Tank Info: 325 6' wide Reef
uncleof6 is offline   Reply With Quote
Unread 07/31/2009, 03:16 PM   #13
luvreefs23
Registered Member
 
Join Date: Feb 2008
Posts: 758
Ive thought about it and asked a few people here at work and i believe i get it now. I want to take the Hot wire and wire nut 2 more lines to feed the other receptacles directly from the original hot wire thats coming in from the braker, same with the neutral, than i can piggy back the grounds as they dont supply power just a means to be grounded so as long as they are all linked and connected to the box im good. Also use the screws and not the plug ins to insure good reliable connection. Sound right?

Thanks


luvreefs23 is offline   Reply With Quote
Unread 07/31/2009, 03:25 PM   #14
evsalty
hmmmmmm
 
Join Date: Jan 2009
Location: NW Mesa, AZ
Posts: 3,531
Quote:
Originally posted by uncleof6
Well you may be lost, but you actually have the recepticles oriented correctly. The NEC does not mention this, but the "inventor" intended the ground terminal of the recepticle to be up, rather than the common usage which is at the bottom.

When I had my walk thru on my first house I asked the PM why they were like that and he said just what you said. I had never ever seen that before and even in my second only the switched outlets were like that lol. I guess doing it the correct way is a sign of a good electrician


evsalty is offline   Reply With Quote
Unread 07/31/2009, 03:26 PM   #15
troylee
Moved On
 
troylee's Avatar
 
Join Date: Oct 2008
Location: here.
Posts: 2,509
Yup.....or tie the grounds together like your doing with the others.....


troylee is offline   Reply With Quote
Unread 07/31/2009, 06:29 PM   #16
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by luvreefs23
Ive thought about it and asked a few people here at work and i believe i get it now. I want to take the Hot wire and wire nut 2 more lines to feed the other receptacles directly from the original hot wire thats coming in from the braker, same with the neutral, than i can piggy back the grounds as they dont supply power just a means to be grounded so as long as they are all linked and connected to the box im good. Also use the screws and not the plug ins to insure good reliable connection. Sound right?

Thanks
Much better


BeanAnimal is offline   Reply With Quote
Unread 07/31/2009, 06:31 PM   #17
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by evsalty
When I had my walk thru on my first house I asked the PM why they were like that and he said just what you said. I had never ever seen that before and even in my second only the switched outlets were like that lol. I guess doing it the correct way is a sign of a good electrician

As Uncle mentioned, many people in the know prefer to have the ground lugs orientated to the top. The idea is that if a conductive material (say a metal ruler) were to fall off of a table and slide down the wall, it would hit the ground first instead of shorting accross the hot and neutral conductors. Code (at least to this point) has not made the distinction and the ground lugs may be either up or down and meet code.


BeanAnimal is offline   Reply With Quote
Unread 07/31/2009, 07:18 PM   #18
luvreefs23
Registered Member
 
Join Date: Feb 2008
Posts: 758
Thanks for the help and diagrams everyone, im picking up my 250 deep dimension marineland tomorrow and wanted to make sure everything is good b4 i put a tank infront of the receptacles and make fixing the outlets nearly impossible.

Dennis


luvreefs23 is offline   Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 01:16 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.