Apex outlet stuck on

I have a outlet on my apex that stays on. I used to have a C02 cylinder plugged in. However now I have a fan plugged in. With both the outlet stays on. I have tried to set it to "manual off" with no luck.

Any ideas what may be wrong?
Thanks


DaFishHead is offline   Reply With Quote
Unread 04/03/2010, 07:13 PM   #2
tamu
Registered Member
 
Join Date: Aug 2001
Location: DFW, TX
Posts: 327
Probably not in outlet 4 or 8, correct?
Those are mechanical relays and can shut off low power factor devices. Try it there if you have not yet.


tamu is offline   Reply With Quote
Unread 04/03/2010, 07:23 PM   #3
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
I have the fan plugged into #1. All of my outlets are full. I can move the fan to 8 but then I have to move something else to #1. So that is not a solution.

Any ideas why the outlets stick on? Any ideas how to fix them?

Thanks


DaFishHead is offline   Reply With Quote
Unread 04/03/2010, 07:33 PM   #4
tamu
Registered Member
 
Join Date: Aug 2001
Location: DFW, TX
Posts: 327
You need to move them, because the low power factor devices (solenoids, fans, etc) need to be plugged into 4 & 8. If they are on the other outlets, there is the possibility like you have found that the triac controlling those outlets can not properly shut the outlet off. The mechanical relay will be able to shut off the solenoid or fan with no problem.

If you plug a light into that outlet you are having an issue with at the moment, it should shut off fine.


tamu is offline   Reply With Quote
Unread 04/03/2010, 07:55 PM   #5
RussM
Registered Member
 
Join Date: Jan 2007
Location: El Cajon, CA
Posts: 7,818
+1 on Tamu's advice. There's nothing wrong with your outlet #1 - this is normal behavior when used with some low-power devices.

Outlets #4 and #8 are relay-controlled. Outlets #1-3 and #5-7 are controlled by a solid-state device called a TRIAC.

TRIACs are good because they never wear out (unlike relays which are mechanical), are silent (no clicking like relays do), and better for devices which have a large startup current draw (like IC660 and some MH ballasts), which can cause arcing inside a relay.

The drawback of a TRIAC is that they require a certain amount of current to be drawn through the TRAIC by the controlled device. If there isn't enough current being drawn, they may not properly shut off properly, so the device stays powered up. Dosing pumps, solenoids, smaller fans, and small powerheads all may cause this.... they turn on just fine, but won't shut off.

So, while the relay-controlled outlets are good for heavy-load items like bigger pumps, bigger chillers, and high-wattage heaters (like 500w & 1000w), they are also excellent to use for those very low power items.


RussM is offline   Reply With Quote
Unread 04/04/2010, 03:45 PM   #6
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
I have four 250 watt heaters three fans and one solenoid controlled by my EB8.

Basically you are telling me that other than outlet #4 and #8 my other outlets are all at risk of staying on?

That STINKS!!!!

Is there a better product that I should have spent my money on?


DaFishHead is offline   Reply With Quote
Unread 04/04/2010, 04:19 PM   #7
tamu
Registered Member
 
Join Date: Aug 2001
Location: DFW, TX
Posts: 327
Quote:
Originally Posted by DaFishHead View Post
Basically you are telling me that other than outlet #4 and #8 my other outlets are all at risk of staying on?

That STINKS!!!!

Is there a better product that I should have spent my money on?
Your heaters will not stick ON on outlets 1-3,5-7. I have my canopy fans and sump fans on those outlets as well and do not have OFF problems. The solenoid is almost a must to be on 4 or 8.

As stated, anything that has a low current draw/power factor has the possibility of not being turned off if running on outlets 1-3,5-7. 250W does not fall into that category.

I suggest if you think this product is junk, then try out the competitor.


tamu is offline   Reply With Quote
Unread 04/04/2010, 06:04 PM   #8
aquamanic
WHO DAT??
 
aquamanic's Avatar
 
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
We're talking devices that draw < 5 watts before you'll have a problem. That's nothing. Try getting light from a 5 watt lightbulb! The advantages of TRIAC outlets far outweigh the 'low power shutoff' problem. Just recognize that its there and work around it. If you're short of relay outlets, just add some other device to your triac outlet along with your low power device to get your current consumption up a little bit. It's not a big deal.


__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's.
Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com
aquamanic is offline   Reply With Quote
Unread 04/04/2010, 07:22 PM   #9
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
Quote:
Originally Posted by tamu View Post

I suggest if you think this product is junk, then try out the competitor.
Ahhh........yeah tamu.....I have money to just throw away.....I'll get right on that.

Here is a post Tamu about how I feel about the competition.

http://www.reefcentral.com/forums/sh....php?t=1711947

The truth be known I love my apex. Still a outlet that sticks open as I said before "Stinks"

Trying to get the outlet so that it is not stuck on. So far I have hooked up a power saw and ran it while I was trying to get the outlet off. No luck

Then, with the help of a power strip, I plugged in three heaters into one outlet and then tried to force the outlet off. No luck with that either. Once the outlet is locked open, is there anyway to get it fixed? Do I have to send it in? Will Neptune take it?


DaFishHead is offline   Reply With Quote
Unread 04/04/2010, 07:30 PM   #10
aquamanic
WHO DAT??
 
aquamanic's Avatar
 
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
Unplug the EB8, wait a few seconds and plug it back in. If that doesn't clear it than something else is wrong. Normally all it takes is manually turning it off.

If you look in the XML Outlet log on the web page (far right), does the outlet show as being OFF?


__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's.
Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com

Last edited by aquamanic; 04/04/2010 at 07:38 PM.
aquamanic is offline   Reply With Quote
Unread 04/04/2010, 07:49 PM   #11
tamu
Registered Member
 
Join Date: Aug 2001
Location: DFW, TX
Posts: 327
Of course they will work with you if it is a hardware issue. You will be amazed the level of customer service. Hardware failures occur all the time with electronics and it's not the end of the world.

You asked the question, I was giving you an option. The Apex destroys the competition (I've run both units).

Don't we all throw money away the minute we start this hobby


tamu is offline   Reply With Quote
Unread 04/04/2010, 07:51 PM   #12
slief
RC Sponsor

 
slief's Avatar
 
Join Date: Sep 2009
Posts: 14,173
Do you have another outlet with the same name as the one that wont turn off?? If 2 outlets have the same name, you might see the same issue.

FWIW. I just added a solenoid to my system a couple days ago and had to put it on 4 or 8 as it wouldnt turn off either on the other outlets. Wasn't a big deal for me as it was the only device on that EB8 that was really low draw.


__________________
Director Customer Support Royal Exclusiv USA
For All Royal Exclusiv & Bubble King questions please refer to our Sponsor forum: http://www.reefcentral.com/forums/fo...play.php?f=745

Current Tank Info: 480G display mixed reef, 90G sump, 90G refugium, 60G display refugium. Check out my build thread: http://www.reefcentral.com/forums/showthread.php?t=1783476
slief is offline   Reply With Quote
Unread 04/04/2010, 08:10 PM   #13
tamu
Registered Member
 
Join Date: Aug 2001
Location: DFW, TX
Posts: 327
Quote:
Originally Posted by slief View Post
Do you have another outlet with the same name as the one that wont turn off?? If 2 outlets have the same name, you might see the same issue.

FWIW. I just added a solenoid to my system a couple days ago and had to put it on 4 or 8 as it wouldnt turn off either on the other outlets. Wasn't a big deal for me as it was the only device on that EB8 that was really low draw.
Good idea to check the naming of the outlet.
It seems as if most controllers run a mixture of triacs and mechanical relays and the issue with shutoff does arise.


tamu is offline   Reply With Quote
Unread 04/05/2010, 03:52 PM   #14
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
Quote:
Originally Posted by aquamanic View Post
Unplug the EB8, wait a few seconds and plug it back in. If that doesn't clear it than something else is wrong. Normally all it takes is manually turning it off.

If you look in the XML Outlet log on the web page (far right), does the outlet show as being OFF?
I will try this tonight. Yes it shows my outlet as off

The name of the stuck outlet is called Fan-A. I have two others named Fan-B and Fan-C but not the exact same name.

I will report tomorrow.

Yes the Customer service that Neptune DESTROYS the competition!!
Curt from Neptune has been amazing when I have had problems.
Let's hope I don't have to bother them.


DaFishHead is offline   Reply With Quote
Unread 04/05/2010, 09:38 PM   #15
gnoles
Equipment Junkie
 
gnoles's Avatar
 
Join Date: Dec 2004
Location: Cleveland, AL
Posts: 288
I'm having this happen on one of my Triacs... I moved two sets of moonlights to instead of the small pump that was on it and still the same thing. I'll pull the plug tomorrow and see if that resets it. This only recently began happening or I'd have all my topoff water in the tank. One thing of note, when I cycled on and off the relay where I moved my autotopoff, the stuck triac turned off to match the controller.


__________________
Gary

"Most people learn by observation, and there are the few who learn by experimentation. And then there are those who actually TOUCH the fire to see if it's really hot." - Anonymous

Current Tank Info: 185 gallon tank, working on automating the sucker!
gnoles is offline   Reply With Quote
Unread 04/06/2010, 03:54 PM   #16
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
Quote:
Originally Posted by aquamanic View Post
Unplug the EB8, wait a few seconds and plug it back in. If that doesn't clear it than something else is wrong. Normally all it takes is manually turning it off.

If you look in the XML Outlet log on the web page (far right), does the outlet show as being OFF?
Well no dice.
No luck for me.
Tried to reset the outlet and I had no luck. Looks like it is time to contact Neptune for more ideas.

Thanks for the ideas.


DaFishHead is offline   Reply With Quote
Unread 04/06/2010, 04:15 PM   #17
pencil3
Registered Member
 
Join Date: Aug 2006
Posts: 282
Count me in too. Happened this morning. Stuck on and can't turn it off unless it's unplugged. Can turn it on then, but not back off. Fine for two weeks before this.


pencil3 is offline   Reply With Quote
Unread 04/06/2010, 08:04 PM   #18
aquamanic
WHO DAT??
 
aquamanic's Avatar
 
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
If you look at your modules at the bottom of the Module Setup web page, does your EB8 show with the same software version number as the rest of your modules?

You might try reloading the firmware to the EB8 and see if that helps. Select the EB8 in the Module Setup page, click the Update Firmware radio button then Submit.


__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's.
Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com
aquamanic is offline   Reply With Quote
Unread 04/06/2010, 08:51 PM   #19
pencil3
Registered Member
 
Join Date: Aug 2006
Posts: 282
All of my eb8s are 006. PM1s PM2s and displays all have matching firmware versions (there are multiples of each installed). Mine is outlet 3, does not matter what is plugged in there it can't be turned off after it is turned on.


pencil3 is offline   Reply With Quote
Unread 04/07/2010, 05:03 AM   #20
aquamanic
WHO DAT??
 
aquamanic's Avatar
 
Join Date: Sep 2009
Location: Baton Rouge, LA
Posts: 5,709
Contact Neptune at support@neptunesys.com . Still feels like a logic problem of some sorts but maybe the EB8 is bad.


__________________
I don't work for Neptune. Please put all questions into forum posts and not PM's.
Visit the Neptune Community Forums for the latest Neptune updates - forum.neptunesystems.com
aquamanic is offline   Reply With Quote
Unread 04/07/2010, 04:14 PM   #21
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
Talked to Neptune. Their customer service is great. I am sending it in for repair.

I hope this is not a common problem.

Reef on!!


DaFishHead is offline   Reply With Quote
Unread 04/14/2010, 06:45 PM   #22
jwalker314
Registered Member
 
Join Date: Aug 2009
Location: Landenberg, PA
Posts: 421
i am having this same problem as well, outlet 5 on mine. Is there any other solution other than disrupting my system and the timers and sending the EB8 away? my tank relies on my APEX to work on a daily basis. thanks.


jwalker314 is offline   Reply With Quote
Unread 04/19/2010, 10:13 PM   #23
DaFishHead
Registered Member
 
DaFishHead's Avatar
 
Join Date: Jul 2008
Location: Milwaukee
Posts: 174
Quote:
Originally Posted by jwalker314 View Post
i am having this same problem as well, outlet 5 on mine. Is there any other solution other than disrupting my system and the timers and sending the EB8 away? my tank relies on my APEX to work on a daily basis. thanks.
None that I know of


__________________
Rule 62. . . . . Don't take yourself so serious.

Current Tank Info: 125 SPS tank that has a 100G sump and drilled to a 29G Seahorse tank. Storing a 65G tank and live stock for a friend.
DaFishHead is offline   Reply With Quote
Unread 04/19/2010, 11:15 PM   #24
kenargo
Premium Member
 
kenargo's Avatar
 
Join Date: Jan 2007
Location: Redmond, WA
Posts: 8,151
Purchase a backup EB8...

I know this might appear over the top by some but (personally) I wouldn't have it any other way; I have too much invested to be without something as critical as a controller.

Early on I would purchase a device as one needed to go in for repair but over time I ended up with a full spare for all critical components.


__________________
Click on my name to visit my homepage and access a collection of AquaController and Apex software, tips, trick and other Q&A including a link to the 'unofficial Apex new users guide' with loads of helpful information and don't forget to put a pin in my location map.

Current Tank Info: 225G, BK 300 Deluxe, Deltec PF601, Precision Marine Kalkreactor, 2-LMIII+6 pumps, SpectraPure UHE, Apex, LunarSim, Tunze 6305s. Mixed reef, clam, fish, etc.
kenargo is offline   Reply With Quote
Unread 04/19/2010, 11:31 PM   #25
slief
RC Sponsor

 
slief's Avatar
 
Join Date: Sep 2009
Posts: 14,173
Quote:
Originally Posted by kenargo View Post
Purchase a backup EB8...

I know this might appear over the top by some but (personally) I wouldn't have it any other way; I have too much invested to be without something as critical as a controller.

Early on I would purchase a device as one needed to go in for repair but over time I ended up with a full spare for all critical components.
Those are some serious words of wisdom right there! Being in the computer business, I know the value of spares. I have 5 EB8's and none of them are spares as all are in use. The fish rots from the head. I need to get myself some spare parts.

All things can and WILL fail. You are dieing from the day you are born. Some will die sooner than others. Some even die at birth (DOA).

Electronics are no different unfortunately.


__________________
Director Customer Support Royal Exclusiv USA
For All Royal Exclusiv & Bubble King questions please refer to our Sponsor forum: http://www.reefcentral.com/forums/fo...play.php?f=745

Current Tank Info: 480G display mixed reef, 90G sump, 90G refugium, 60G display refugium. Check out my build thread: http://www.reefcentral.com/forums/showthread.php?t=1783476
slief is offline   Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 04:10 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.