Chinese box shocked me today!
While making adjustments on my frag rack I noticed a little zing when I placed my hand in the water. I thought for sure it was my Hydor wave makers, I had one short on me last year. While investigating I came to the conclusion that when a part of my body touches the box and then I touch the water I would get shocked. anyone else have this experience? or something similar? the box is about 12 inches from the top of the tank (14in from the waterline). I have been thinking about going back to T-5's
|
01/18/2019, 07:29 PM | #2 |
Registered Member
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
|
Dont be so sure that the light is the problem...
The chassis is hopefully grounded and as such is simply the ground connection required to complete the circuit... The problem could still be in the tank..
__________________
Who me? |
01/20/2019, 03:59 PM | #3 |
Registered Member
Join Date: Feb 2012
Location: Cullman,alabama
Posts: 329
|
|
01/20/2019, 06:34 PM | #4 | |
Registered Member
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
|
Quote:
If not gfci protected its better to not have a ground probe. The only valid use for a ground probe is to cause the gfci to trip the instant a fault develops...Without one the equipment stays live until you become the path to ground and trip the gfci
__________________
Who me? |
|
01/21/2019, 06:36 AM | #5 |
Registered Member
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
|
I concur with mcgyvr on both post, too many times we blame our lights for shocking us, when they are just providing a grounding path.
|
01/25/2019, 03:01 PM | #6 |
Registered Member
Join Date: Feb 2012
Location: Cullman,alabama
Posts: 329
|
A ground probe takes any stray voltage to ground. Really has nothing to do with a gfi.
|
|
|