Reef Central Online Community

Go Back   Reef Central Online Community > General Interest Forums > Lighting, Filtration & Other Equipment
Blogs FAQ Calendar

Notices

User Tag List

Reply
Thread Tools
Unread 10/08/2015, 05:22 PM   #1
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Thumbs down GFCI Question - receptacle install fail

So #1 my house is old and I don't have a ground wire. I guess my box might be grounded IDK i'm know nothing about electrical. #2 my wires are aluminum not copper = fail. This is my setup now. So instead of installing a breaker(assuming those wires are not copper either) I bought these shack buster portable GFCI adapters and will plug in my apex and another power surge to it here is a picture. Does this have me covered? If so I will just return this receptacle outlet tomorrow!



(btw the second one is actually plugged into the wall outlet but with a 1" extension cable like this one)

I wasn't able to fit both into the wall outlet flush b.c they were too bulky.

Thanks!



Last edited by expo703; 10/08/2015 at 05:29 PM.
expo703 is offline   Reply With Quote
Unread 10/08/2015, 07:30 PM   #2
Gorgok
Registered Member
 
Gorgok's Avatar
 
Join Date: Feb 2011
Location: Cypress, Texas
Posts: 1,904
If you lose power do those come back on with it, or need to clicky button to fix them (the latter is common in my experience)? If its the latter i would take the risk of shock over the inconvenience of clicky buttons...

Or run a new wire to that outlet and do it right.


Gorgok is offline   Reply With Quote
Unread 10/08/2015, 07:45 PM   #3
Harry_Y
Registered Member
 
Harry_Y's Avatar
 
Join Date: Jan 2011
Location: NY
Posts: 454
Can you just wore up a dedicated circuit?


__________________
.

180 Gallon Reef with Basement Sump,
Apex Controller, Hamilton Cebu Sun Light,
Lifereef Skimmer and Calcium Reactor.
Harry_Y is offline   Reply With Quote
Unread 10/08/2015, 07:53 PM   #4
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Quote:
Originally Posted by Gorgok View Post
If you lose power do those come back on with it, or need to clicky button to fix them (the latter is common in my experience)? If its the latter i would take the risk of shock over the inconvenience of clicky buttons...

Or run a new wire to that outlet and do it right.
I have yet to lose power..but I have closed the circuit on the breaker while they were on and then turned it back on from the breaker no problem without clicking any reset buttons. Isnt that the same thing?


expo703 is offline   Reply With Quote
Unread 10/08/2015, 07:53 PM   #5
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Quote:
Originally Posted by Harry_Y View Post
Can you just wore up a dedicated circuit?
I have no clue how to do that I didnt even know what a GFCI was before reading about them on this forum! ;]


expo703 is offline   Reply With Quote
Unread 10/08/2015, 11:18 PM   #6
oreo57
Registered Member
 
Join Date: Apr 2013
Posts: 1,793
Quote:
Originally Posted by expo703 View Post
So #1 my house is old and I don't have a ground wire. I guess my box might be grounded IDK i'm know nothing about electrical. #2 my wires are aluminum not copper = fail. Does this have me covered? If so I will just return this receptacle outlet tomorrow!
well considering the above "having you covered" is a bit sketchy.. BUT that little preaching aside..

GFCI's do protect you from large shocks regardless if a ground is present or not..Main function is to rapidly "sense" a difference in the load balance..

So it certainly is better than not having one..

As a side note there are more "elegant" solutions:

http://www.drsfostersmith.com/produc...m?pcatid=17878


oreo57 is offline   Reply With Quote
Unread 10/08/2015, 11:56 PM   #7
Gorgok
Registered Member
 
Gorgok's Avatar
 
Join Date: Feb 2011
Location: Cypress, Texas
Posts: 1,904
Quote:
Originally Posted by expo703 View Post
I have yet to lose power..but I have closed the circuit on the breaker while they were on and then turned it back on from the breaker no problem without clicking any reset buttons. Isnt that the same thing?
Yep, that should be the same.

Some of the really cheap stuff i've seen need to be reset each time they are plugged in or power trips... Basically worthless junk.


Gorgok is offline   Reply With Quote
Unread 10/09/2015, 09:07 AM   #8
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Quote:
Originally Posted by Gorgok View Post
Yep, that should be the same.

Some of the really cheap stuff i've seen need to be reset each time they are plugged in or power trips... Basically worthless junk.
Gotcha - so I should be covered I mean it looks pretty ugly but @ least its safer and if I plug my Apex powerbar and another surge directly into that I should be fine right?


expo703 is offline   Reply With Quote
Unread 10/09/2015, 09:15 AM   #9
reelredfish
Registered Member
 
Join Date: Oct 2012
Location: DFW,Area
Posts: 798
You may not like this but without a ground I would be concerned also the larger issue at hand is the fact that this is alum. wire.

They stopped using it for a reason it caused a lot of house fires back in the day. If you own the home you may want to plan out having a new box put in and all new wires ran. I understand this would be a large job but better to be safe than sorry.


reelredfish is offline   Reply With Quote
Unread 10/09/2015, 09:38 AM   #10
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Quote:
Originally Posted by reelredfish View Post
You may not like this but without a ground I would be concerned also the larger issue at hand is the fact that this is alum. wire.

They stopped using it for a reason it caused a lot of house fires back in the day. If you own the home you may want to plan out having a new box put in and all new wires ran. I understand this would be a large job but better to be safe than sorry.
I'm aware about that and no way we are going to do that lol that could cost 8-15k plus we do not own the house.

I think the ground wire is probably on the back of the outlet box screwed on making the whole box grounded or @ least that is how I read they used to do it back in the day.


expo703 is offline   Reply With Quote
Unread 10/09/2015, 12:15 PM   #11
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
Aluminum back in the 70's sucked, it was brittle and broke. Todays aluminum is made to copper standards, but not made in #12 or #10. If your home is not grounded and a receptacle is changed it needs to be a GFCI with a sticker that states this receptacle is not grounded. When you make that change since there are no more CU/Al receptacles you will need to pigtail the receptacle with #12 copper wire and then use purple wirenuts made for cu/al connections. Older devices had screws that where made from brass and where soft and connected to aluminum wire, todays screws on devices are steel and a not compatible with aluminum wire. And like someone mentioned GCFI doesn't stop you from getting shocked, but hopefully it safes your life.


alton is offline   Reply With Quote
Unread 10/11/2015, 08:44 AM   #12
Icefire
Seasoned reefer
 
Icefire's Avatar
 
Join Date: Jan 2007
Location: In Quebec, Canada
Posts: 3,653
Quote:
Originally Posted by oreo57 View Post
So it certainly is better than not having one..
I would never put a GFCI on something give life support to something, including fish.

They will trip for no reason in the middle of the night and kill your tank.

Better use a ground probe + regular breaker in my opinion


__________________
Temp 80F, PH 8.5-8.0, Alk 6.8-7.2, Ca 430, Mg 1700, NO3 0-0.25, PO4 0.04, 34.4 PPT
Lights @ 100% all others, 35% White

Current Tank Info: 60g Cube, 120lbs live rocks, Hydra52 2x120W, 2 MP40+ 1 MP10 @ 70%, Phosban 550 GFO+Carbon, 200W Heater, SWC Skimmer, Kalk ATO, 150 gpd RODI
Icefire is offline   Reply With Quote
Unread 10/11/2015, 09:34 AM   #13
jrp1588
Registered Member
 
jrp1588's Avatar
 
Join Date: Nov 2009
Location: Evansville, IN
Posts: 1,864
Quote:
Originally Posted by Icefire View Post
I would never put a GFCI on something give life support to something, including fish.

They will trip for no reason in the middle of the night and kill your tank.

Better use a ground probe + regular breaker in my opinion
I've had power outages that last days and didn't lose the tank. Granted, I eventually got the heater and a pump running off a generator, but there was probably a good 12 hours without any power at all. I doubt a night without power would hurt much unless you keep your house really really cold, and your tank is small.


jrp1588 is offline   Reply With Quote
Unread 10/11/2015, 04:20 PM   #14
expo703
Registered Member
 
Join Date: Sep 2015
Posts: 311
Well I have a APEX hooked up now so I will get notified if they ever turn off for some reason..


expo703 is offline   Reply With Quote
Unread 10/11/2015, 08:30 PM   #15
Icefire
Seasoned reefer
 
Icefire's Avatar
 
Join Date: Jan 2007
Location: In Quebec, Canada
Posts: 3,653
Quote:
Originally Posted by expo703 View Post
Well I have a APEX hooked up now so I will get notified if they ever turn off for some reason..
If the Apex is on the same GFCI, you'll get notified only when power is back on


__________________
Temp 80F, PH 8.5-8.0, Alk 6.8-7.2, Ca 430, Mg 1700, NO3 0-0.25, PO4 0.04, 34.4 PPT
Lights @ 100% all others, 35% White

Current Tank Info: 60g Cube, 120lbs live rocks, Hydra52 2x120W, 2 MP40+ 1 MP10 @ 70%, Phosban 550 GFO+Carbon, 200W Heater, SWC Skimmer, Kalk ATO, 150 gpd RODI
Icefire is offline   Reply With Quote
Unread 10/11/2015, 10:10 PM   #16
sleepydoc
Registered Member
 
sleepydoc's Avatar
 
Join Date: Oct 2011
Location: Minneapolis, MN
Posts: 3,907
Quote:
Originally Posted by Icefire View Post
I would never put a GFCI on something give life support to something, including fish.

They will trip for no reason in the middle of the night and kill your tank.

Better use a ground probe + regular breaker in my opinion
Regular breakers are designed to protect the wiring in your house, not you, and ground probes don't perform the same function.

I would never have a tank without a GFI outlet. Of all the GFI outlets I've had in houses over the last 20 years, I have never had a single one trip in the middle of the night for no reason. I have however had one trip when I did something stupid.


__________________
~~~~~~~~~~~~~~~~~~~~~
120 gallon, coast to coast overflow w/beananimal overflow. Waveline DC 10000 II return pump, 40 gal sump, Octopus XS200 skimmer, T5 lighting
sleepydoc is offline   Reply With Quote
Unread 10/12/2015, 06:03 AM   #17
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
I believe the Op stated there was not a ground wire? So a grounding probe is worthless, a metal box nailed to a wood stud is not a grounding means.


alton is offline   Reply With Quote
Unread 10/12/2015, 06:44 AM   #18
billdogg
Registered Member
 
billdogg's Avatar
 
Join Date: Apr 2008
Location: Grove City, Ohio
Posts: 10,806
Quote:
Originally Posted by sleepydoc View Post
Regular breakers are designed to protect the wiring in your house, not you, and ground probes don't perform the same function.

I would never have a tank without a GFI outlet. Of all the GFI outlets I've had in houses over the last 20 years, I have never had a single one trip in the middle of the night for no reason. I have however had one trip when I did something stupid.
What Sleepydoc said


X 1,000,000,000


__________________
I'll try to be nice if you try to be smarter!
I can't help that I grow older, but you can't make me grow up!

Current Tank Info: 120 mixed reef with 40b sump, RO 150 skimmer, AI Sol Blue x 2, and a 60g Frag Tank with 100g rubbermaid sump. 2 x Kessil A360w lights, BM curve 5 skimmer
billdogg is offline   Reply With Quote
Unread 10/12/2015, 09:17 PM   #19
Icefire
Seasoned reefer
 
Icefire's Avatar
 
Join Date: Jan 2007
Location: In Quebec, Canada
Posts: 3,653
How many person did you heard that died from a shock in an aquarium?
Like you said GFCI were installed because people did stupid thing in bath/shower.

The day you'll have real electricity leaking in a saltwater tank @ 35ppt / 0.20 Ohms/meter, that is a direct short and your breaker will trip. Not talking about "stray voltage, induced voltage"

The only way to have GFCI on a tank is to have separated outlet so if one trip, you still have other powerhead, Sometimes 2-3 hours with no flow will be enought to have fish gasping for air.

Just for fun, there is a few thread about GFI tripped, dead tank like this one, which is a desaster: http://www.reefcentral.com/forums/sh....php?t=2449045


__________________
Temp 80F, PH 8.5-8.0, Alk 6.8-7.2, Ca 430, Mg 1700, NO3 0-0.25, PO4 0.04, 34.4 PPT
Lights @ 100% all others, 35% White

Current Tank Info: 60g Cube, 120lbs live rocks, Hydra52 2x120W, 2 MP40+ 1 MP10 @ 70%, Phosban 550 GFO+Carbon, 200W Heater, SWC Skimmer, Kalk ATO, 150 gpd RODI

Last edited by Icefire; 10/12/2015 at 09:27 PM.
Icefire is offline   Reply With Quote
Unread 10/13/2015, 07:40 AM   #20
alten78
Registered Member
 
alten78's Avatar
 
Join Date: Nov 2004
Location: Sheffield Lake, OH
Posts: 1,231
Quote:
Originally Posted by Icefire View Post
How many person did you heard that died from a shock in an aquarium?
Like you said GFCI were installed because people did stupid thing in bath/shower.
How many people haven't died because a GFCI tripped? The most recent that mine tripped is when one of my halides wiring got corroded and kept tripping the outlet. I would have never had known this was happening if it weren't for the GFCI. Would I have gotten shocked or worse if it wasn't there? Maybe, but I don't want to find out. Lots of moisture and salt around a lot of electrical equipment and power, As far as I'm concerned, I prefer the safety of myself or one of my family members over what is in my glass box.


__________________
When life gives you lemons, make lemonade. Then find a person where life gave them vodka and have a party. ~ Ron White

Current Tank Info: 120g SPS dominated
alten78 is offline   Reply With Quote
Unread 10/13/2015, 08:10 AM   #21
RWEngineer
Registered Member
 
Join Date: Aug 2015
Posts: 120
Quote:
Originally Posted by sleepydoc View Post
regular breakers are designed to protect the wiring in your house, not you, and ground probes don't perform the same function.

I would never have a tank without a gfi outlet. Of all the gfi outlets i've had in houses over the last 20 years, i have never had a single one trip in the middle of the night for no reason. I have however had one trip when i did something stupid.

+1


RWEngineer is offline   Reply With Quote
Unread 10/13/2015, 08:15 AM   #22
jrp1588
Registered Member
 
jrp1588's Avatar
 
Join Date: Nov 2009
Location: Evansville, IN
Posts: 1,864
Quote:
Originally Posted by Icefire View Post
Sometimes 2-3 hours with no flow will be enought to have fish gasping for air.
That's gotta be in a heavily overstocked tank. I went half a day once, in the winter, in a basement. Didn't lose a single fish. I don't even think the fish noticed. They just acted like they always do during lights out.

After that, I was just running my heater and a single powerhead for 2 more days. That reminds me, I need to check if my 2-stroke backup tank generator still works.


jrp1588 is offline   Reply With Quote
Unread 10/13/2015, 02:23 PM   #23
sleepydoc
Registered Member
 
sleepydoc's Avatar
 
Join Date: Oct 2011
Location: Minneapolis, MN
Posts: 3,907
GFCI Question - receptacle install fail

Quote:
Originally Posted by Icefire View Post
How many person did you heard that died from a shock in an aquarium?
Like you said GFCI were installed because people did stupid thing in bath/shower.

The day you'll have real electricity leaking in a saltwater tank @ 35ppt / 0.20 Ohms/meter, that is a direct short and your breaker will trip. Not talking about "stray voltage, induced voltage"

The only way to have GFCI on a tank is to have separated outlet so if one trip, you still have other powerhead, Sometimes 2-3 hours with no flow will be enought to have fish gasping for air.

Just for fun, there is a few thread about GFI tripped, dead tank like this one, which is a desaster: http://www.reefcentral.com/forums/sh....php?t=2449045

Never heard from the people that died. They're dead.

A breaker trips at 15-20 amps. I'm not sure what your definition of 'real electricity' is, but ventricular fibrillation is induced between 100 and 200 mA. There was a tragic case many years ago where a kid passed out at a party and his friends thought it would be funny to wire him up to an electric cord to 'shock him awake.' They had a switch that they briefly flipped on every once in a while to give him a shock. Except that the switch was actually on and they were briefly flipping it off. They electrocuted him quite nicely, but the circuit breaker never blew. To be blunt, anyone claiming that a 15 amp breaker will protect people from electrocution is at best misinformed, at worst ignorant and reckless.

If you'd worried about a GFCI tripping and the tank dying from loss of power, a ground probe could easily do the same thing with the circuit breaker, so advocating the use of ground probes in place of GFCIs fails to address the problem.

Stray voltage is meaningless; it's how much current that voltage can drive that is the issue. Likewise induced voltage can be just as dangerous as 'regular' voltage. Note that a GFCI will not protect you from induced voltages.

I do not claim that GFCIs are flawless. Nor will they eliminate every shock, and thankfully not every shock that occurs without a GFCI will be fatal, but they will dramatically improve your odds.

Splitting a tank between two circuits is never a bad idea; I've heard plenty of cases where something else on the circuit caused it to trip, a bad power bar, etc. anything to add redundancy is helpful. Compromising safety is just not an option in my opinion.

If you choose not to protect yourself, that's your own choice, but I find advising people to forego recommended, proven (and in some cases legally required) safety measures based on an incomplete understanding of the physics and physiology to be irresponsible.


__________________
~~~~~~~~~~~~~~~~~~~~~
120 gallon, coast to coast overflow w/beananimal overflow. Waveline DC 10000 II return pump, 40 gal sump, Octopus XS200 skimmer, T5 lighting

Last edited by sleepydoc; 10/13/2015 at 02:34 PM.
sleepydoc is offline   Reply With Quote
Unread 10/14/2015, 07:24 PM   #24
Harry Muscle
Registered Member
 
Harry Muscle's Avatar
 
Join Date: Oct 2004
Location: Mississauga, ON
Posts: 169
Quote:
Originally Posted by sleepydoc View Post
Never heard from the people that died. They're dead.

A breaker trips at 15-20 amps. I'm not sure what your definition of 'real electricity' is, but ventricular fibrillation is induced between 100 and 200 mA. There was a tragic case many years ago where a kid passed out at a party and his friends thought it would be funny to wire him up to an electric cord to 'shock him awake.' They had a switch that they briefly flipped on every once in a while to give him a shock. Except that the switch was actually on and they were briefly flipping it off. They electrocuted him quite nicely, but the circuit breaker never blew. To be blunt, anyone claiming that a 15 amp breaker will protect people from electrocution is at best misinformed, at worst ignorant and reckless.

If you'd worried about a GFCI tripping and the tank dying from loss of power, a ground probe could easily do the same thing with the circuit breaker, so advocating the use of ground probes in place of GFCIs fails to address the problem.

Stray voltage is meaningless; it's how much current that voltage can drive that is the issue. Likewise induced voltage can be just as dangerous as 'regular' voltage. Note that a GFCI will not protect you from induced voltages.

I do not claim that GFCIs are flawless. Nor will they eliminate every shock, and thankfully not every shock that occurs without a GFCI will be fatal, but they will dramatically improve your odds.

Splitting a tank between two circuits is never a bad idea; I've heard plenty of cases where something else on the circuit caused it to trip, a bad power bar, etc. anything to add redundancy is helpful. Compromising safety is just not an option in my opinion.

If you choose not to protect yourself, that's your own choice, but I find advising people to forego recommended, proven (and in some cases legally required) safety measures based on an incomplete understanding of the physics and physiology to be irresponsible.
I couldn't agree more.

Harry


Harry Muscle is offline   Reply With Quote
Unread 10/15/2015, 06:01 AM   #25
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
Sleepydoc covered most of it and is fairly accurate except the part of a breaker tripping at 15 - 20 amps. A 20 amp breaker will trip most times at 20 amps if the panel is 87F. In the winter and your panel is outside or in the garage with a temp of 40 or below and it can take 30 to 40 amps depending on the temperature to trip. I have seen several plugs and cords that burned because they were rated at 15 amps and could not hold up during the large current draw from a bad heater that created a giant resister out of a friends aquarium. Remember our tanks are insulated holding all voltages and currents until we make the grounding path, at that time hopefully out GFCI's will protect us not from shock, but from death. One last thing if you have been shacked from your tank you where probably wearing shoes which help insulate and protected you from the major part of the shock. Water and electricity are a dangerous mix, please take extra steps to protect yourself. One rule is before you place your had in your tank, tap the top of the water with a finger before just reaching in. It is better to get a little zap than a big shock.


alton is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 04:23 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.