11/01/2017, 02:04 AM | #376 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Chiller WONT STOP chilling.
Man I’ve looked just about everywhere, Allen just about everywhere, and to no avail. I really hope I can find some help HERE.
I own a 1/10hp eco plus water chiller. The model before they were assembled in China. Made in 12/12. Anyways, i thought I had fixed the problem as it wasn’t working for quite a good while here recently AFTER this problem had persisted, but NOW its doing it again. So basically, I can set my temp for 68,69,70 whatever I feel like having it at, and when I come back after a few hours, it’s down to 63 & would go lower if I left it alone. It’s so strange because the machine REGISTERS the cooler temps right on the front of the lCD. It’s saying 62, I press set, and it’s set at 70. How is this possible? ESPECIALLY since it seems to have fixed itself a while back. The “chiller” light turns off and the “external heater” light stays on, with the fan blowing as it’s lowering in temps. When it’s workin correctly, it will completely shut off (besides the LCD display of course) once it’s hit the target temperature. I really hope somebody knows a thing or two about this. please oh please, help me. |
11/01/2017, 06:49 AM | #377 |
RC Mod
|
Sounds like a contactor is sticking closed. This can happen for a variety of reasons. If it's happening on the main circuit board, you may have to replace the board. Or you could pick up a temp controller, (Ranco comes to mind), and let it do the controlling.
__________________
Jesse I'm not saying I'm Batman. I'm just saying nobody has ever seen me and Batman in a room together. |
11/01/2017, 03:04 PM | #378 | |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Quote:
|
|
11/01/2017, 03:05 PM | #379 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
I've got pics of all the inside's of the chiller just dont kknow how to post pics here.
|
11/01/2017, 05:32 PM | #380 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Basically here is what is happening. When I plug it in if my water temperature is higher than the set it will automatically turn on with the chiller light flashing like it should when it is chilling. If I turned it on and the set temp is higher than the actual temp then the power light just stays on until it hits that higher temperature and the external heater light turns on solidly. From that point the water temperature will continue to drop and drop until I unplug it. I'm also using an exterior temperature probe for backup and the temperatures are always the same on the LCD screen and my probe. So basically once my temperature has rise past my set temperature I'm plugging it back in to start that chilling light up to see if maybe it would turn off like it's supposed to but it's just not. I need to know how the voltage flows through this controller so I know at which point this contact would be giving me problems. Do you know how the electricity flows from the wall through the controller and where I could find this? Is it the little black box or the copper thing wrapped in yellow? Where is it one of those little cylinders that soldered on to the PCB? I'm not afraid to solder things if needed I just need to know what part to fix.
|
11/02/2017, 02:14 PM | #381 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
The external heater light Ive just found out is actually for the plug in the back of the machine. It's a two prong outlet that I tested today. I do not use an external heater but when that light comes on on the machine, that port / Outlet becomes energized and is delivered power so that if I were to use a heater inside the tank, it would slowly warm up the water. I do not understand why my machine is acting this way rather than just turning off and letting the temperature rise on its own. Today I set it at 67 and within a few hours it was down to 62. I am so confused as to why it's not just turning off and now is thinking it needs to rely on actual heat source to bring the water temperature up.
|
11/04/2017, 03:50 AM | #382 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Doesn’t anybody AT ALL know how to get it out of this mode where it thinks it needs a heater to warm the water temp.? Why does it continue to chill?!?!
|
11/06/2017, 07:33 PM | #383 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Bump. Please help me if you can.
|
11/12/2017, 02:39 PM | #384 |
Registered Member
Join Date: Nov 2017
Posts: 41
|
Well I gave up. Just gonna out it on a timer for 1 hour on and 2 hours off.
|
05/31/2018, 10:57 AM | #385 |
Registered Member
Join Date: Jan 2007
Location: Puerto Rico
Posts: 838
|
My Artica 1/4 stopped working. When i turn it on the fan turn on and remains on. I recalibrated it and also put the temp to 60 degrees but the compressor didn't turn on neither.
I called JBJ and they stated it is a bad compressor. i will take it to a refrigerator service to see if they can certify it is the compressor or the relay. in the meantime can anyone suggest me a good quality chiller brand just in case?
__________________
125 Gal. Reef Tank, Skimmer SRO-1000SSS (Old), Aquamaxx EM-200, Chiller Artica 1/4, BRS GFO/Carbon Reactor, Sunpower 6x80 Watt., Actinic ReefBrites, 2 Jebao RW-15, 3/4 Sea Swirl, HY-5000 Return Pump, Current Tank Info: 125 Gal. Reef, Chiller 1/4, Skimmer SRO SSS-1000 (Old), Aquamaxx EM-200, Aqua C UV, Actinic ReefBrites, Kore 5th. Doser, APEX Full |
05/31/2018, 11:01 AM | #386 |
Registered Member
Join Date: Nov 2002
Location: Miller Place, NY
Posts: 7,206
|
__________________
250 gallon mixed reef, 2 Reefbreeder's Photon V 2, Deepwater BLDC 12, DAS EX-3 Skimmer, MTC mini cal, 2-3/4" Sea Swirls, Aquacontroller & 6 Tunze pumps. |
06/01/2018, 07:50 AM | #387 | ||
Registered Member
Join Date: Jan 2007
Location: Puerto Rico
Posts: 838
|
Quote:
Quote:
Just to update I took the case off and found that the cables from the relay touched the metal and burned out. Can somebody identify me what is the black part that comes with the cables that go to the relay at the right side? Here is a pic for reference.
__________________
125 Gal. Reef Tank, Skimmer SRO-1000SSS (Old), Aquamaxx EM-200, Chiller Artica 1/4, BRS GFO/Carbon Reactor, Sunpower 6x80 Watt., Actinic ReefBrites, 2 Jebao RW-15, 3/4 Sea Swirl, HY-5000 Return Pump, Current Tank Info: 125 Gal. Reef, Chiller 1/4, Skimmer SRO SSS-1000 (Old), Aquamaxx EM-200, Aqua C UV, Actinic ReefBrites, Kore 5th. Doser, APEX Full |
||
06/03/2018, 06:24 AM | #388 | |
Ver. 2.1
Join Date: Mar 2005
Location: Rehoboth, MA
Posts: 1,803
|
Quote:
http://www.jbjlighting.com/pdfs/Aqua...riesManual.pdf
__________________
Pete "I never make mistakes... I thought I did once, but I was wrong" Current Tank Info: In the process - http://reefcentral.com/forums/showthread.php?t=2661614 |
|
06/04/2018, 05:42 AM | #389 | |
Registered Member
Join Date: Jan 2007
Location: Puerto Rico
Posts: 838
|
Quote:
For my surprise I cut the burn cables and joined them and the Chiller is working again like a champ. Weird the support I received from JBJ. After explaining my problem they first stated I had a bad controller and I said that is impossible because I can work and set the temp in the panel, then they said I had a bad relay, I asked if the relay is bad why the fan is all ways on and they said its a relationship and finally they said SORRY but you have a bad Compressor but your chiller is old so you must replace it. That kind of support of guessing options got me thinking as I was going to invest I an upgrade as the summer is hot over here in PR but to be honest I haven't had to use their support in 7 years so that says enough of their equipment.
__________________
125 Gal. Reef Tank, Skimmer SRO-1000SSS (Old), Aquamaxx EM-200, Chiller Artica 1/4, BRS GFO/Carbon Reactor, Sunpower 6x80 Watt., Actinic ReefBrites, 2 Jebao RW-15, 3/4 Sea Swirl, HY-5000 Return Pump, Current Tank Info: 125 Gal. Reef, Chiller 1/4, Skimmer SRO SSS-1000 (Old), Aquamaxx EM-200, Aqua C UV, Actinic ReefBrites, Kore 5th. Doser, APEX Full |
|
06/04/2018, 05:58 AM | #390 | |
Ver. 2.1
Join Date: Mar 2005
Location: Rehoboth, MA
Posts: 1,803
|
Quote:
My JBJ chiller is over 13 years old, and the only issue I ever had was shortly after I purchased it. I had a problem with the fuse holder on the rear for the incoming power supply. They sent me a new cord and fuse holder. Since then no problems whatsoever! If the need ever arises, I wouldn't hesitate to by another JBJ chiller.
__________________
Pete "I never make mistakes... I thought I did once, but I was wrong" Current Tank Info: In the process - http://reefcentral.com/forums/showthread.php?t=2661614 |
|
06/04/2018, 08:05 AM | #391 |
Registered Member
Join Date: Jan 2007
Location: Puerto Rico
Posts: 838
|
Thanks Buddy....
__________________
125 Gal. Reef Tank, Skimmer SRO-1000SSS (Old), Aquamaxx EM-200, Chiller Artica 1/4, BRS GFO/Carbon Reactor, Sunpower 6x80 Watt., Actinic ReefBrites, 2 Jebao RW-15, 3/4 Sea Swirl, HY-5000 Return Pump, Current Tank Info: 125 Gal. Reef, Chiller 1/4, Skimmer SRO SSS-1000 (Old), Aquamaxx EM-200, Aqua C UV, Actinic ReefBrites, Kore 5th. Doser, APEX Full |
09/04/2018, 12:07 PM | #392 |
Registered Member
Join Date: Aug 2007
Location: cerritos, CA//las vegas, nevada
Posts: 567
|
Hi I have an old current 1/15 chiller and it was working fine yesterday, but this morning it decided to not work at all. The chiller itself was really hot and it stopped making it's signature loud hum, now it just has a low hum and it is NOT chilling the water. The water is still still flowing through it but the chiller itself turns on but doesn't seem to do anything. Any idea?
|
09/04/2018, 12:22 PM | #393 | |
Ver. 2.1
Join Date: Mar 2005
Location: Rehoboth, MA
Posts: 1,803
|
Quote:
Not sure, but see if any local HVAC guys could check it out for you.
__________________
Pete "I never make mistakes... I thought I did once, but I was wrong" Current Tank Info: In the process - http://reefcentral.com/forums/showthread.php?t=2661614 |
|
09/04/2018, 12:43 PM | #394 | |
Registered Member
Join Date: Aug 2007
Location: cerritos, CA//las vegas, nevada
Posts: 567
|
Quote:
|
|
09/04/2018, 12:58 PM | #395 | |
Ver. 2.1
Join Date: Mar 2005
Location: Rehoboth, MA
Posts: 1,803
|
Quote:
__________________
Pete "I never make mistakes... I thought I did once, but I was wrong" Current Tank Info: In the process - http://reefcentral.com/forums/showthread.php?t=2661614 |
|
09/07/2018, 09:20 PM | #396 | |
Registered Member
Join Date: Aug 2007
Location: cerritos, CA//las vegas, nevada
Posts: 567
|
Quote:
|
|
09/08/2018, 09:24 AM | #397 |
RC Mod
|
Personally, I would get it fixed. You need to be moving a certain amount of air across the coils. Not enough, and your cooling may not be enough. Too much may cause freezing problems. Have him go over it while he has it. Check Freon levels and give the coils a cleaning.
__________________
Jesse I'm not saying I'm Batman. I'm just saying nobody has ever seen me and Batman in a room together. |
10/03/2018, 06:34 AM | #398 |
Registered Member
Join Date: Feb 2008
Location: FL
Posts: 3
|
So this morning I woke up to an odd issue. Compressor in the chiller is always on. If I turn the entire unit off, there is a semi violent shake down as it turns off. When I turn it back on, the compressor comes back on automatically, BUT the A/C light on the control panel doesn't turn on and temp shows 75-78 even though set temp is 78. Model is a TECO CA 200.
__________________
75 Gallon w/ Custom Sump and Chiller Livestock: Hippo and Yellow Tang, Foxface, 2 False Perculas, 3 Pajama Cardinals, 1 Bangai Cardinal, 2 bonded Firefish, 1 Coral Banded Shrimp, Hermits and Snails. Current Tank Info: 30G, Coralife 150W light, Marineland 30G Canister Filter |
02/02/2019, 10:39 AM | #399 |
Registered Member
Join Date: Nov 2015
Posts: 1
|
Question here....
I have a Coralife 1/4HP chiller with a problem. When i plug it in the display allows me to set the temp i want and it also tells me the water temp. The problem is that it doesn't seam to turn on the compressor to cool the water like it should. Any ideas as to why that may be? |
04/26/2019, 06:48 PM | #400 |
Registered Member
Join Date: Jun 2018
Posts: 60
|
Need some serious help please! My JBJ Arctica 1/10 chiller seems to be acting up. The issue is that the unit will chill and then for some reason out of nowhere the unit will say 90 degrees and the cooling indicator light continues to blink. I'm puzzled, the only way I'm able to fix this issue is either change the temp setting or unplug the chiller and plug it back in.
|