Stray Voltage Brain Teaser

So here is a brain teaser for you on stray voltage.

Echotech MP10's adding 2 volts....

External 12 volt power adapter for Apex adding 9 volts. Thats with probes, skimmer, return, heaters, and ato unplugged.

Everything with contact to the water unplugged including the apex power supply and echotechs and I get 5 volts...

New battery in volt meter (for those about to ask). Add a ground probe using same ground I am testing with and it drops to zero...


I am thinking something in my house wiring is causing strange reading.


Just for reference I have 30 years experience in electronics....


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's

Last edited by MHG; 12/15/2014 at 01:38 PM. Reason: spelling
MHG is offline   Reply With Quote
Unread 12/15/2014, 02:07 PM   #2
Gandolfe
Registered Member
 
Gandolfe's Avatar
 
Join Date: May 2005
Location: New Port Richey,Florida
Posts: 849
I had a powerhead go bad and was adding stray voltage...actually got shocked a few times feeding my fish


Gandolfe is offline   Reply With Quote
Unread 12/15/2014, 02:11 PM   #3
fermentedhiker
Registered Member
 
fermentedhiker's Avatar
 
Join Date: Aug 2013
Location: Maine
Posts: 382
I'd double check the ground you are using against another circuit. It sounds like a poor connection in the ground you are using and that throwing off your reading.


fermentedhiker is offline   Reply With Quote
Unread 12/15/2014, 02:48 PM   #4
MisterP
Registered Member
 
Join Date: Jul 2013
Location: TN
Posts: 401
Quote:
Originally Posted by MHG View Post
Add a ground probe using same ground I am testing with and it drops to zero...
If you have 30 years experience in electronics you should know your ground and neutral circuit in your home is screwed up. You don't have a zero reference any more which is why when everything is unplugged you still get 5 V potential.



Last edited by MisterP; 12/15/2014 at 02:49 PM. Reason: sp
MisterP is offline   Reply With Quote
Unread 12/15/2014, 02:50 PM   #5
MisterP
Registered Member
 
Join Date: Jul 2013
Location: TN
Posts: 401
Let me re-phrase slightly.... the ground neutral circuit on the fish tank is screwed up not your entire house....I wouldn't think.

Have you measured other circuits in your home?

Is it bonded....ground/neutral?


MisterP is offline   Reply With Quote
Unread 12/15/2014, 04:04 PM   #6
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
What do you get when you go from the grounding probe/slot to the grounded probe/slot on your duplex receptacle? And what voltage do you get going from your ungrounded probe/slot first to your grounded and then switching over to your grounding probe/slot? My next question is what type of room lighting do you have in this room, and does your voltage change when you turn it off? And or is your tank lights on when you perform your test?



Last edited by alton; 12/15/2014 at 04:14 PM.
alton is offline   Reply With Quote
Unread 12/15/2014, 05:06 PM   #7
n2585722
Registered Member
 
Join Date: Aug 2008
Location: Cedar Park, Tx
Posts: 1,072
Is you lighting on when you get this voltage?


n2585722 is offline   Reply With Quote
Unread 12/16/2014, 08:11 AM   #8
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
Quote:
Originally Posted by MisterP View Post
If you have 30 years experience in electronics you should know your ground and neutral circuit in your home is screwed up. You don't have a zero reference any more which is why when everything is unplugged you still get 5 V potential.
Wow. A bit harsh. For the record I said electronics not as an electrician. Outlets test fine. No hot or neutral swap and it certainly did not magically swap on its own as this was all in the millivolt range a few months ago when I tested it last. However thanks for the suggestion.

Quote:
Originally Posted by MisterP View Post
Let me re-phrase slightly.... the ground neutral circuit on the fish tank is screwed up not your entire house....I wouldn't think.

Have you measured other circuits in your home?

Is it bonded....ground/neutral?
I get the same reading when measuring off my tank outlet (on mu sub panel) as well as one of the homes original outlets off the main CB panel.

When I moved in I had a new 200 amp service put in and it was all bonded to two new ground rods as well as the water main. But I will double check those connections...

I am tending to think it is a grounding issue...

Quote:
Originally Posted by alton View Post
What do you get when you go from the grounding probe/slot to the grounded probe/slot on your duplex receptacle? And what voltage do you get going from your ungrounded probe/slot first to your grounded and then switching over to your grounding probe/slot? My next question is what type of room lighting do you have in this room, and does your voltage change when you turn it off? And or is your tank lights on when you perform your test?
You may need to rephrase this. You lost me... I have incandescent in that room and the lights are almost never on.

Quote:
Originally Posted by n2585722 View Post
Is you lighting on when you get this voltage?
Yes and no. Voltage is there when DIY LED's are plugged in or un plugged.



Just for more reference. The DT is running off a 3K UPS. The apex power supply is not. It is there only to tell the Apex that there was a power outage. Both are running off the same sub panel.

Also I have a EB8 Module in my fish room and it runs off the same ups.


If I bypass the UPS I still get the same issue, so I dont think that has anything to do with it.


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's
MHG is offline   Reply With Quote
Unread 12/16/2014, 08:55 AM   #9
MisterP
Registered Member
 
Join Date: Jul 2013
Location: TN
Posts: 401
Quote:
Wow. A bit harsh. For the record I said electronics not as an electrician. Outlets test fine. No hot or neutral swap and it certainly did not magically swap on its own as this was all in the millivolt range a few months ago when I tested it last. However thanks for the suggestion.
Sorry not trying to be harsh just came out wrong....My thoughts don't always get put on paper the best way. I'm not an electrician either but an EE and I figured if your worked with electronics that long it should be easy to troubleshoot.



Is that outlet grounded to common ground or do you have a common ground and separate "local" grounds, if you will, such that you lose your common reference point and now have a potential difference between the 2 grounds?


MisterP is offline   Reply With Quote
Unread 12/16/2014, 08:56 AM   #10
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
Quote:
Originally Posted by MisterP View Post
Sorry not trying to be harsh just came out wrong....My thoughts don't always get put on paper the best way. I'm not an electrician either but an EE and I figured if your worked with electronics that long it should be easy to troubleshoot.



Is that outlet grounded to common ground or do you have a common ground and separate "local" grounds, if you will, such that you lose your common reference point and now have a potential difference between the 2 grounds?
I will open the panels and eyeball them...Thanks.


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's
MHG is offline   Reply With Quote
Unread 12/16/2014, 09:03 AM   #11
stk731
Registered Member
 
Join Date: Aug 2013
Posts: 193
run a dedicated ground all the way to the panel


stk731 is offline   Reply With Quote
Unread 12/16/2014, 09:08 AM   #12
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
I will confirm it has one. But I believe it does...


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's
MHG is offline   Reply With Quote
Unread 12/16/2014, 11:12 AM   #13
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
On your duplex receptacle you have three slots, U shaped is the grounding, large slot is the grounded, and small slot is the ungrounded. I always check for voltage between the large slot and U shaped slot to make sure there is no floating or loose neutral. Then I check for voltage from the large slot and the small slot which you should have 120+/- volts and then going from the small slot to the U shaped slot you should have the exact same voltage. Also this requires PPE using gloves and safety glasses minimum. Remember the only place you can bond the grounding conductors and grounded conductors is at the service. All sub panels shall have a separate grounding bar, and the grounded conductors shall have an insulated bar for terminations. If you combine the two on the same bar and use a grounding probe I have seen where the sub panel will use your tank as a grounding means.


alton is offline   Reply With Quote
Unread 12/16/2014, 11:15 AM   #14
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
The reason why I asked about your lights was I have had issues with Fluorescent and MH fixtures and stray voltage in the past.


alton is offline   Reply With Quote
Unread 12/20/2014, 02:47 PM   #15
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
Quote:
Originally Posted by alton View Post
On your duplex receptacle you have three slots, U shaped is the grounding, large slot is the grounded, and small slot is the ungrounded. I always check for voltage between the large slot and U shaped slot to make sure there is no floating or loose neutral. Then I check for voltage from the large slot and the small slot which you should have 120+/- volts and then going from the small slot to the U shaped slot you should have the exact same voltage. Also this requires PPE using gloves and safety glasses minimum. Remember the only place you can bond the grounding conductors and grounded conductors is at the service. All sub panels shall have a separate grounding bar, and the grounded conductors shall have an insulated bar for terminations. If you combine the two on the same bar and use a grounding probe I have seen where the sub panel will use your tank as a grounding means.
We'll you started to say what I have read in some of my electrical reference manuals that only the main service is grounded and the sub panels are not. Or is it that only place neutral is bonded to ground is the main panel. But then you say that have a separate ground. Sub panels sold here in my do not come with a ground bus. Only a neutral...

My sub is connected to the main via a 3 wire mc cable. No copper ground. So the enclosures are bonded by the shielding. Should I run a ground from the sub to the water main?


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's

Last edited by MHG; 12/20/2014 at 03:10 PM. Reason: Spelling
MHG is offline   Reply With Quote
Unread 12/21/2014, 01:18 AM   #16
tonyscoots84
Registered Member
 
tonyscoots84's Avatar
 
Join Date: Mar 2006
Location: Howell, NJ
Posts: 322
your best bet is process of elimination. Kill the breaker which your tank is on and then see if you still have stray voltage. Then go from there. If you still do keep shutting breakers till you find the culprit and go from there. I hope you find the issue, it can be very frustrating especially after having a new panel installed and can imagine how much they charged you for it ....


__________________
120 Gallon RR tank
Sfligoi 2 x 400w radium bulbs w/4 t5's

Current Tank Info: 120 gallon single overflow, Sflligoi 2x 400w radium with 4 t5's, 2 mp40's, tunze ato, skimz monster 203, eheim 1262 return, SPS all the way :)
tonyscoots84 is offline   Reply With Quote
Unread 12/21/2014, 08:47 AM   #17
dkeller_nc
Registered Member
 
dkeller_nc's Avatar
 
Join Date: Mar 2013
Location: Central NC
Posts: 5,062
Keep in mind that you cannot accurately measure "water voltage" with a voltmeter in this way (placing one probe in the tank water, and the other into a ground on a wall socket) because you're attempting to measure a floating ground.

What you need to do instead is set the meter for AC current, then place one probe in the tank water and the other in the ground conductor in the receptacle. If you measure less than 5-10 milliamps or so, you don't have a "stray voltage" problem, and your tank equipment is correctly functioning.

If you do get an amperage reading of >10 milliamps, you may well have a pump motor whose insulation has broken down, or a heater that's shorted to the water.

By the way - keep in mind that a lot of us with an electrical background think that a "grounding probe" is a bad idea because it converts a voltage potential to a current actual.


dkeller_nc is offline   Reply With Quote
Unread 12/21/2014, 01:26 PM   #18
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
Quote:
Originally Posted by tonyscoots84 View Post
your best bet is process of elimination. Kill the breaker which your tank is on and then see if you still have stray voltage. Then go from there. If you still do keep shutting breakers till you find the culprit and go from there. I hope you find the issue, it can be very frustrating especially after having a new panel installed and can imagine how much they charged you for it ....
Thanks. I think folks are missing the original intent of the post. I am quite familiar with the trouble shooting process. The brain teaser is how can something not even connected to the water produce voltage in the water. The MP10's for example are producing between .8 and 2.8 volts. The Apex power supply is producing almost 10 volts. My LED Drivers are producing from .5 to 3 volts depending on how bright they are set...

Quote:
Originally Posted by dkeller_nc View Post
Keep in mind that you cannot accurately measure "water voltage" with a voltmeter in this way (placing one probe in the tank water, and the other into a ground on a wall socket) because you're attempting to measure a floating ground.

What you need to do instead is set the meter for AC current, then place one probe in the tank water and the other in the ground conductor in the receptacle. If you measure less than 5-10 milliamps or so, you don't have a "stray voltage" problem, and your tank equipment is correctly functioning.

If you do get an amperage reading of >10 milliamps, you may well have a pump motor whose insulation has broken down, or a heater that's shorted to the water.

By the way - keep in mind that a lot of us with an electrical background think that a "grounding probe" is a bad idea because it converts a voltage potential to a current actual.
Well the current on the volt meter only reads in series with DC current or with an inductive probe around the AC cords. With several shocking voltages present in tanks I have tried the method you described and never measured any current.

Voltage does not get converted to current rather current is drawn. The probe provides a path to ground and can of course result in a bad thing and a high current transfer if no path previously existed and the source of the voltage was an actual conductive path and not the typical inductive lower voltage leaks. Also the a probe masks a problem and one should check regularly for stray voltage. But having been shocked in the past, I prefer to run them and check monthly for voltages without the probe in the water. Also providing that path to ground for any current will trip the GFI...

Again, I think the original brain teaser is being missed...


I am putting together a drawing that will show what I have found so far...


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's
MHG is offline   Reply With Quote
Unread 12/22/2014, 01:41 AM   #19
Reef Automation
Registered Member
 
Reef Automation's Avatar
 
Join Date: Mar 2007
Location: Apple Valley, CA.
Posts: 5
Ground loop Voltage

Hello, I had an issue like this once at work. In my situation voltage was seen on the ground leg of several outlets in the building even after all the breakers in the main breaker panel were off. We found that someone in the past decided it was a good idea to use the neutral bus in the main breaker panel to bond ground lines, and also found ground lines bonded on the neutral bus.

Interestingly enough, we also found a very very slight stray voltage in our building ground from a "grounding bond" made from the local phone service utility hookup on the outside of our building.

If you can put the grounds on the ground bus and the neutrals on the neutral bus your original issue may be eliminated. hope this helps brother.



Last edited by Reef Automation; 12/22/2014 at 01:52 AM.
Reef Automation is offline   Reply With Quote
Unread 12/22/2014, 06:24 AM   #20
alton
Registered Member
 
alton's Avatar
 
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
Here is a picture of a service panel with the neutral bar grounded, and then sub panel with the neutral bar ungrounded. If the grounding conductors are on the neutral bar in the sub panel you have a chance to have voltage and more important current at your receptacles. What Reef Automation said is correct


Attached Files
File Type: pdf panel.pdf (25.9 KB, 13 views)
alton is offline   Reply With Quote
Unread 12/22/2014, 07:42 AM   #21
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
Attached is a drawing of what I have. What I have found is the guy who ran the sub panel used BX with a bonding strip rather than MC with an independent ground. However the two panels are bonded together and ohm out with no problem. However if I lose a neutral on my sub panel this bonding is not going to handle and significant current so I need to fix this. I dont know if NEC allows for me to bond my sub independent to ground. The water main is 10' away and I can also sink independent grounds into the earth just outside the wall. I believe NEC will allow for that but I don't know. Either way they are currently bonded and is not the source of the 5 volts I have with nothing plugged in as I have discovered that...

I have three outlets running to my DT. Two are on a 3KVUPS and one is not. I needed the one not on a UPS because my apex needs to monitor the power so it knows when it is out and adjust the loads so the UPS lasts as long as possible. All three outlets test fine with a outlet tester. All three ohm out to ground with each other and with one outlet I have near by that runs off the main.

However when trouble shooting I noticed that if I disconnect one of the outlets from my UPS (located in the basement near my sub panel) and plug it into a GFI next to my frag system near the sub panel it pops the GFI. It will not let me reset it. However if I plug them both into the GFi, I do not pop it. It does not matter which one I plug into the UPS and which one I plug into the GFI. In either case the GFI trips. So while testing voltage in the DT If I plug outlet #1 into either the UPS or the GFI I get 0.0XXX volts in the DT. When I plug in outlet #2 in I get 3-5 volts (goes up and down). Even with nothing plugged into outlet # 2. Keep in ming both outlet 1+2 plug into a UPS in the basement and run upstairs to two outlets behind my DT. So if I have my apex plugged into outlet#1 and nothing plugged into outlet#2 I get 3-5v in my DT water. This was not the case when this was installed 4 years ago and has not been the case up until a month or so ago.

So That feed running from my UPS to my DT is causing the voltage with nothing in the water. Don't know how but don't care. It is an issue so I have abandoned that outlet as it can not be fixed with out draining and removing the DT.

So continuing on with my stray voltage trouble shooting starting at 0.0xx or lower voltage...

here is what each item adds to my voltage and the original point of my original questions.
  • MP10's .6-3 volts (varies as pumps surge)
  • Apex 12v power supply 5 volts
  • DIY LED Drivers 0 volts when on but ar zero percent. 1-2 volts whan ramped up to 100%

Still with nothing contacting the water turned on. Heaters, skimmer, return pumps all off...and un-plugged. Now I know most aquarium stray voltage are inductive so I get the MP10's But DC drivers where the transformers are mounted 20" away is throwing me for a loop and the 5 volts from a 12 power supply that is over a foot away is confusing as hell...

I do have a bad skimmer pump. That is putting 16 volts into the water. I have ordered a new one...And all the other strange ancillary voltages (heaters, and return pump) are no longer an issue with just the one feed removed from the equation.


Attached Images
File Type: jpg Electrical.jpg (38.3 KB, 13 views)
__________________
MHG (LIRA Member)
60G Cube, Kessil 360's

Last edited by MHG; 12/22/2014 at 07:47 AM. Reason: spelling
MHG is offline   Reply With Quote
Unread 12/22/2014, 08:03 AM   #22
dkeller_nc
Registered Member
 
dkeller_nc's Avatar
 
Join Date: Mar 2013
Location: Central NC
Posts: 5,062
Quote:
Originally Posted by MHG View Post
Well the current on the volt meter only reads in series with DC current or with an inductive probe around the AC cords. With several shocking voltages present in tanks I have tried the method you described and never measured any current.
...
Keep in mind that most multimeters will indeed measure AC current without the use of an inductive probe, though I'll take your word for it if yours does not. However, if your meter isn't measuring any current, and you can actual feel current if you put your hand in the water (and not just a transient shock from a static discharge), it may be time to replace the multimeter.


dkeller_nc is offline   Reply With Quote
Unread 12/22/2014, 08:28 AM   #23
MHG
Registered Member
 
Join Date: Feb 2011
Posts: 2,919
My current DT tank has no feeling of shock. But my old frag system shocked me. as well as a friends... Because of my profession I have a wide variety of multi meters at my disposal. including a Fluke 190 scope meter (I have 8 of them and whenever I sign one out I get the same readings).

Again, I appreciate the assistance. And I by no means know everything and I am for certain learning things every day on this issue. My main focus on this thread is to see if anyone can assist me with explaining the voltages from items not touching the water...


__________________
MHG (LIRA Member)
60G Cube, Kessil 360's
MHG is offline   Reply With Quote
Unread 12/27/2014, 02:13 PM   #24
Christian J
Registered Member
 
Join Date: Aug 2010
Posts: 152
Couldn't alternating magnetic fields outside the tank induce a voltage?


Christian J is offline   Reply With Quote
Unread 12/28/2014, 09:28 PM   #25
Utwo229
Registered Member
 
Join Date: Sep 2012
Location: Ocala, Fl
Posts: 30
Hi, just saw your post. I'll try to answer what I can. I am an electrician.

Attached is a drawing of what I have. What I have found is the guy who ran the sub panel used BX with a bonding strip rather than MC with an independent
However the two panels are bonded together and ohm out with no problem.

Can't tell from your drawing, but in the sub-panel the neutral should not be bonded to the case and the ground bar should. Bonding strap on BX is code compliant...

However if I lose a neutral on my sub panel this bonding is not going to handle and significant current so I need to fix this.

Not sure why you'd loose a neutral, but if you do then you should have a short circuit and the breaker will trip.

I dont know if NEC allows for me to bond my sub independent to ground.

No. Not allowed. The equipment grounding conductor (ground) needs to connect all metal parts to the service main. Only the service main is bonded to the grounded conductor (neutral). The neutral shall never ever be bonded to ground except at the service main. No time to explain electrical theory here, but that's the way it's done.

The water main is 10' away and I can also sink independent grounds into the earth just outside the wall. I believe NEC will allow for that but I don't know. Either way they are currently bonded and is not the source of the 5 volts I have with nothing plugged in as I have discovered that...

Attaching independent grounding electrodes (ground rods) is a bad idea. The entire system ground within your house must have the same voltage reference to the earth so it should only be connected in one place. Hopefully your water pipes are all connected to the system ground, but there is no telling if they may have an interruption at a valve or meter between where you are and where they are bonded.


Utwo229 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 12:43 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.