Setting up my ato I have a small 24v pump and wallwart I am using would I need to put a relay on the float since it is a small pump or could I wire it directly through float.


Mdj is offline   Reply With Quote
Unread 12/12/2017, 03:57 PM   #2
der_wille_zur_macht
Team RC Member
 
der_wille_zur_macht's Avatar
 
Join Date: Sep 2003
Location: NY
Posts: 17,749
I don't think it's ever good practice to put power through a float switch, they should really be operating at signal levels only. In other words, use a relay. Assuming you're using one of the standard float switches seen in this hobby (Madison M8000 or a knockoff), they're pretty fragile, we need to do whatever we can to protect them.


__________________
Inconveniencing marine life since 1992

"It is my personal belief that reef aquaria should be thriving communities of biodiversity, representative of their wild counterparts, and not merely collections of pretty specimens growing on tidy clean rock shelves covered in purple coralline algae." (Eric Borneman)
der_wille_zur_macht is offline   Reply With Quote
Unread 12/12/2017, 05:14 PM   #3
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
That's what I figured was hoping I might be able to save a plug with a small pump will go get like 3v plug in and relay thanks for your help


Mdj is offline   Reply With Quote
Unread 12/12/2017, 05:17 PM   #4
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
That's what what I figured was hoping to save myself a plug with a small pump guess I will go get a small 3v wallwart and a relay. This hobby sure takes slot of plug spots


Mdj is offline   Reply With Quote
Unread 12/12/2017, 06:16 PM   #5
cwetherford
Registered Member
 
Join Date: Nov 2013
Posts: 1
Thanks for the insight... I’m doing the same thing


cwetherford is offline   Reply With Quote
Unread 12/12/2017, 06:28 PM   #6
outy
Moved On
 
Join Date: Oct 2004
Location: auburn CA
Posts: 4,021
autotopoff.com is the best place to get cheap ATO parts. mine are a decade old and still in use.

do it right the first time, and be done. No worrying on a very important piece of electronics


outy is offline   Reply With Quote
Unread 12/12/2017, 06:40 PM   #7
der_wille_zur_macht
Team RC Member
 
der_wille_zur_macht's Avatar
 
Join Date: Sep 2003
Location: NY
Posts: 17,749
You can use the 24v power supply for both the pump and the signal circuit (assuming you have an appropriate relay), you just don't want the full current powering the pump to be running through the switch.


__________________
Inconveniencing marine life since 1992

"It is my personal belief that reef aquaria should be thriving communities of biodiversity, representative of their wild counterparts, and not merely collections of pretty specimens growing on tidy clean rock shelves covered in purple coralline algae." (Eric Borneman)
der_wille_zur_macht is offline   Reply With Quote
Unread 12/13/2017, 04:45 AM   #8
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
Would I just need to run a resistor in the line to float to lower current. Wallwart t off wire resistor to floats back to relay then other side of t back to relay. What type of resistor would be best to restrict power from wallwart through float switches ?


Mdj is offline   Reply With Quote
Unread 12/13/2017, 05:59 AM   #9
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
You do not need a resistor at all..The coil of the relay is basically the resistor
The relay "draws" (pulls) only the current it needs and that small current travels through the float.
The float is capable of switching the small current the relay is drawing to operate but typically the current that a pump is drawing is too much for the float to switch reliably..


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 12/13/2017, 06:39 AM   #10
der_wille_zur_macht
Team RC Member
 
der_wille_zur_macht's Avatar
 
Join Date: Sep 2003
Location: NY
Posts: 17,749
The signal side of the relay and the power side would be wired in parallel. They'd both get their own 24v from the power supply, and the current through each branch of the circuit would be completely independent.


__________________
Inconveniencing marine life since 1992

"It is my personal belief that reef aquaria should be thriving communities of biodiversity, representative of their wild counterparts, and not merely collections of pretty specimens growing on tidy clean rock shelves covered in purple coralline algae." (Eric Borneman)
der_wille_zur_macht is offline   Reply With Quote
Unread 12/13/2017, 07:48 AM   #11
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
Here is a quick diagram of your wiring..


Attached Images
File Type: jpg ATO 24VDC.jpg (29.9 KB, 29 views)
__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 12/13/2017, 12:46 PM   #12
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
Thanks I can run that guess my brain was just thinking the 24v would be going through switch didn't know it would only send what the relay needed. Guess that's why I don't work with electric much normally.


Mdj is offline   Reply With Quote
Unread 12/14/2017, 05:32 AM   #13
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
yep thats a very common misconception.

An LED though on the other hand needs that resistor (or constant current power source) to "spoon feed" it the current it needs or it will let out the magic smoke..


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 12/14/2017, 10:28 AM   #14
der_wille_zur_macht
Team RC Member
 
der_wille_zur_macht's Avatar
 
Join Date: Sep 2003
Location: NY
Posts: 17,749
Quote:
Originally Posted by Mdj View Post
Thanks I can run that guess my brain was just thinking the 24v would be going through switch
To be clear, the full 24v will actually be applied to the switch. It's not the voltage that's a problem (within reason), it's the current the pump would pull. When you wire loads in parallel, each gets the full voltage, but each parallel branch of the circuit is completely independent in terms of current. The pump can pull all the current it needs, and the switch will only see the current required to hold the relay closed (which is typically very small).


__________________
Inconveniencing marine life since 1992

"It is my personal belief that reef aquaria should be thriving communities of biodiversity, representative of their wild counterparts, and not merely collections of pretty specimens growing on tidy clean rock shelves covered in purple coralline algae." (Eric Borneman)
der_wille_zur_macht is offline   Reply With Quote
Unread 12/14/2017, 11:34 AM   #15
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
Quote:
Originally Posted by der_wille_zur_macht View Post
To be clear, the full 24v will actually be applied to the switch. It's not the voltage that's a problem (within reason), it's the current the pump would pull. When you wire loads in parallel, each gets the full voltage, but each parallel branch of the circuit is completely independent in terms of current. The pump can pull all the current it needs, and the switch will only see the current required to hold the relay closed (which is typically very small).
I went with the assumption that they really didn't mean voltage but good you posted it when I was too lazy to


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 12/15/2017, 02:30 PM   #16
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
Think it makes more since to me know so since I am hooking up 2 floats all I need to do is split wire going to float from diagram above then run both floats to the relay so they will work independently for a fail safe. I am also wanting to put a float on reservoir to kill the pump if it gets to low on water could I put this float before other 2 floats so they run through it or should I run another relay to kill pump if water gets low in resevoir


Mdj is offline   Reply With Quote
Unread 12/15/2017, 02:42 PM   #17
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
Quote:
Originally Posted by Mdj View Post
Think it makes more since to me know so since I am hooking up 2 floats all I need to do is split wire going to float from diagram above then run both floats to the relay so they will work independently for a fail safe. I am also wanting to put a float on reservoir to kill the pump if it gets to low on water could I put this float before other 2 floats so they run through it or should I run another relay to kill pump if water gets low in resevoir
All 3 in series.. One in ATO fresh tank flipped over (inverted operation)
Note you can either just flip the whole sensor over to invert but IMO its always better to keep the spot where the wire enters the connector dry at all times and you can flip the "bobber" upside down by removing the plastic ring (or whatever your version has) to invert the function..
I always run my wires through some vinyl tubing that fits snugly over the threaded portion right where the wire enters and even apply a bit of silicone to seal it even better..
The can/do fail because of a faulty seal so I do that to hopefully mitigate that issue..


Attached Images
File Type: jpg ATO 24VDC V2.jpg (24.8 KB, 13 views)
__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 12/15/2017, 11:01 PM   #18
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
Ok now I am a bit confused what is purpose of backup switch if ran in series if 1st float sticks won't it stop the secondary float from working if it is stuck open or am I missing something that is why I assumed running in parallel would be way to go so all switches would work independently even if failure occurred will the other switches work as a backup if switch one sticks in series


Mdj is offline   Reply With Quote
Unread 12/16/2017, 04:54 AM   #19
perkint
Registered Member
 
Join Date: Jan 2014
Location: Robin hood country, UK
Posts: 817
If they are in parallel, any one of the float switches being closed will run the pump (so if one sticks, the pump still runs). If they are in series, they all need to be closed, so any one sticking will only run the pump until the next one opens the circuit

Tim


perkint is offline   Reply With Quote
Unread 12/16/2017, 06:34 AM   #20
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
Ok so the fail safe is intended to keep display from flooding but it will not protect me if a float sticks not allowing the pump to kick on from loosing to much water in display will it or am I just way over thinking this i am going to use the diagram with the 3 floats from above should float 1 be set just higher than 2 or did I get it backwards


Mdj is offline   Reply With Quote
Unread 12/16/2017, 04:48 PM   #21
perkint
Registered Member
 
Join Date: Jan 2014
Location: Robin hood country, UK
Posts: 817
As you say, running them in series with one float higher than the other prevents over filling but not under filling. To be honest, IMO if you want that, use a controller (an Arduino nano).

Tim


perkint is offline   Reply With Quote
Unread 12/16/2017, 05:54 PM   #22
Mdj
Registered Member
 
Join Date: Aug 2017
Posts: 56
I am eventually going to tackle a controller but for now I must go without I think I am going to need a whole lot more research to diy a arduino controller and box controllers are just way out of my budget as of now but this will at least prevent me from topping tank off manually twice a day thanks so much for your help


Mdj is offline   Reply With Quote
Unread 12/18/2017, 01:41 PM   #23
perkint
Registered Member
 
Join Date: Jan 2014
Location: Robin hood country, UK
Posts: 817
To be fair, developing an ATU controller is a pretty good first Arduino project

Tim


perkint is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 11:58 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2024 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.