Posts: 219
|
earth leakage circuit breaker & bubble king
I have a Bubble King skimmer sm250 with dc pump. It will trip any outlet I plug it into. My tank is on a dedicated panel with GFI Breakers. Royal Exclusiv has emailed me and said it needs to be on an ELCB. The electrician and the search button says ELCB have been replaced by the GFI breaker. But with the help of google they still sell ELCB. I am looking for reassurance before I email RE back.
The breakers on the left run the tank. The ones on the right are for the room lights and vent fans. Thanks!! ![]() |
![]() |
![]() |
![]() |
#2 |
Registered Member
![]() Join Date: Mar 2010
Location: Calabasas, CA
Posts: 1,501
|
This is correct. Same thing happened with my 240w DC pumps by another manufacturer.
__________________
Current tank: 340g AGE peninsula |
![]() |
![]() |
![]() |
#3 |
Registered Member
Join Date: Jan 2005
Location: Zuehl, Texas
Posts: 4,460
|
If what I just read online, ELCB breakers are made to protect the motor not you
|
![]() |
![]() |
![]() |
#4 |
Registered Member
Join Date: May 2009
Location: Westslope CO
Posts: 219
|
|
![]() |
![]() |
![]() |
#5 |
Registered Member
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
|
A GFCI will trip around 5mA..
The drive used in these motors seems to have leakage current in excess of that so you want a ELCB that will allow a higher leakage current (up to 30mA) without nuisance tripping that a RCD/GFCI will suffer from. |
![]() |
![]() |
![]() |
#6 |
Registered Member
Join Date: May 2009
Location: Westslope CO
Posts: 219
|
Thank you, that is an explanation I can understand.
|
![]() |
![]() |
![]() |
#7 |
Registered Member
![]() Join Date: Mar 2010
Location: Calabasas, CA
Posts: 1,501
|
What he (mcgyvr)said!
There may be another option as well: the manufacturer of my pump recommended I wind the pump power cable around a ferrite ring to choke the leakage current. Unfortunately, the ring I managed to find did not work well enough to prevent nuisance trips of the GFCI.