Electrical Safety and Your Tank

I just wanted to offer up a quick guide to electricity and our tanks to help out people with little to no experience on the subject. I do NOT claim to know it all, there are far more intelligent people on this site with more accolades than me. I am a electrician working primarily in industrial controls and power for 10 years now. I have gotten a ton of info on this site, and have become addicted to this hobby. I can't offer a lot on reefs yet, but I wanted to help out on what I can.

Safety Measures You can take:

GFCI's

A gfci operates by measuring the current between the ungrounded ("hot") conductor and the grounded conductor (neutral). If it becomes unbalanced it will trip and turn off the circuit. Meaning, if the circuit is pulling 5 amps, and .005 amps strays to anything other than the return path of the neutral, ie the grounding conductor or you, it will trip.

A gfci is primarily to protect you. It will also protect the tank, but it is there to keep you alive. It is HIGHLY RECOMMENDED!! It can come in a power strip, recptacle or breaker. They all work the same, one may last longer than the other.

Surge Protector's

These typically come in power strips that are cheap and come in power strips. They inhibit a voltage spike to protect equipment that it is supplying power for. They do not offer any protection for you.

A surge protector may be a hazardous piece of equipment, that a gfci, afci, or circuit breaker may not (highly probable) stop from causing a fire or damage. Please, please do a ALOT OF RESEARCH before you decide to use this or not. There is a risk to using them that IMO doesn't outweigh the benefits of protecting my tank equipment. Thanks to Westom for schooling me on the danger of these here
-->http://reefcentral.com/forums/showth...urge+protector

Some more threads that a surge protector didn't go well:
http://www.atlantareefclub.org/forum...ad.php?t=55174
http://www.reefsanctuary.com/forums/...r-weekend.html
http://www.esdjournal.com/techpapr/P...OR%20FIRES.doc

Ground Probes

A ground probe should be used in your tank. It is used for stray voltages. (see bottom for stray voltages). A ground probe will put your tank at the same potential as your grounding conductor in your electrical system. IMO, you should use it with a gfci. The probe will put the tank at the same potential as your grounding conductor for tripping your circuit breaker. However during the time it takes to clear your breaker, your tank will be experiencing high current levels. If a gfci is used in conjunction with a ground probe, it will trip the circuit before the current reaches higher levels and may not even trip the circuit breaker.

Afci Breakers

Afci breakers are newer. The NEC is starting to require these breakers in many new locations in residential homes. A afci stands for arc fault circuit interrupter. A afci does not replace a gfci! A afci monitors the circuit for any arcing on ungrounded to grounded or ungrounded to grounding conductor faults. They use a circuit board to monitor the current sine wave, recognizing a short circuit fault and opening the circuit. They are not cheap, but can be used as a great safety feature. They compliment a gfci recptacle. I am not using one yet, but will be shortly. In theory you could have water splash and produce a arc fault from ungrounded to grounded and never trip a gfi.

A link:
http://www.pfeiffereng.com/The%20Arc...nterrupter.pdf

Stray Voltages:

Many people grab a meter and think they have a stray voltage in their tank. When in reality they don't. The BEST way to ensure you don't have any stray voltage is a gfci and ground probe in your tank. Stray voltage readings are meaningless without current readings.

To properly test your tank: take one probe on your meter while set on VAC to the grounding conductor and one probe to water surface of your tank. If you do not have a grounding probe you WILL read a voltage.

When I did my results were 24vac to the grounding conductor. When I did it to the grounded (nuetral) conductor I got 39 volts, and to the ungrounded conductor I got 69 volts. My current readings were 0 amps. These voltage readings are harmless. They are shown because of induction and difference of potential of two separate conductors. Stray voltage should be a concern when it gets closer to 105 vac or more, but a gfci and ground probe WILL alleviate any of those concerns of having stray voltage and not knowing it. If a gfci trips, you can troubleshoot from there.

After a ground probe is installed my tank the readings were the following:

Tank to ground conductor- 0 volts
Tank to neutral conductor- .112 volts (the difference would be the distance to the panel bonding conductor, it is of no concern)
Tank to hot conductor-123 volts

I will say it one more time, if you believe you are having stray voltage issues, and do not have a gfci at minimum on the tank power supply, GET A GFCI RECPTACLE OR POWER STRIP. It is not a cover all solution, but it does cover a majority.

Tips:

Heat is a great warning sign for any electrical problem. Check your cords, power strips,and power supplies by hand for any warm or warmer than normal spots, while checking for frays, knicks, cuts, etc. Do this monthly or more.

A gfci does not last forever, consider changing it yearly or every 2 years. Use the push to test once a month to make sure it is still functioning.

IMO, the perfect setup is a gfci recptacle, non surge suppressor dj power strip, and a tank ground probe. But check multiple sources before you make your decision.


__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill

Last edited by staindsoul; 10/01/2012 at 08:42 PM.
staindsoul is offline   Reply With Quote
Unread 10/01/2012, 09:27 PM   #2
sleepydoc
Registered Member
 
sleepydoc's Avatar
 
Join Date: Oct 2011
Location: Minneapolis, MN
Posts: 3,907
It was never clear to me what the purpose of a grounding probe was on top of a GFCI. In general, voltage isn't the issue, current is. As you indicated, you had 69 volts, but that voltage was unable to generate a current. If you have a GFCI and it generates more than 5 mA, it should trip, right?

As far as the fish in the tank go, as long as the voltage is static and uniform (which it should be in a conductive fluid,) they shouldn't know the difference. Voltage is a potential which has to be measured relative to something else. By convention, we arbitrarily define ground as '0,' but if you're sitting in the tank and have no clue what ground is, it shouldn't matter.

+1 the comments on GFCIs. Get an outlet or a GFCI extension cord before you find out why you need them!


__________________
~~~~~~~~~~~~~~~~~~~~~
120 gallon, coast to coast overflow w/beananimal overflow. Waveline DC 10000 II return pump, 40 gal sump, Octopus XS200 skimmer, T5 lighting
sleepydoc is offline   Reply With Quote
Unread 10/01/2012, 09:47 PM   #3
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
Yep a gfci trips on a 5ma imbalance between hot and nuetral. The ground probe puts the tank at same point of reference, which is what the nec tries to do in all locations, that are not meant to carry current, to trip the source breaker. If you run a ground probe without a gfi and do have a fault, your gonna fry your inhabitants. If you don't run a ground probe or gfi and have a fault or true stray voltage your inhabitants should be ok, think squirrel on a high voltage line or bird on the same, but you are going to shock or electrocute yourself when you put your hand in the tank. If your body is grounded when you stick your hand in the tank, YOU will become the ground probe.


Quote:
Originally Posted by sleepydoc View Post
It was never clear to me what the purpose of a grounding probe was on top of a GFCI. In general, voltage isn't the issue, current is. As you indicated, you had 69 volts, but that voltage was unable to generate a current. If you have a GFCI and it generates more than 5 mA, it should trip, right?

As far as the fish in the tank go, as long as the voltage is static and uniform (which it should be in a conductive fluid,) they shouldn't know the difference. Voltage is a potential which has to be measured relative to something else. By convention, we arbitrarily define ground as '0,' but if you're sitting in the tank and have no clue what ground is, it shouldn't matter.

+1 the comments on GFCIs. Get an outlet or a GFCI extension cord before you find out why you need them!



__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill
staindsoul is offline   Reply With Quote
Unread 10/02/2012, 05:28 AM   #4
lwillis22
Registered Member
 
Join Date: Sep 2012
Posts: 303
So where can we get a grounding probe? I am not sure what these are.


lwillis22 is offline   Reply With Quote
Unread 10/02/2012, 05:38 AM   #5
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
There is really nothing wrong with surge protectors or power strips when used properly.

Most of you like to "hide" your ugly outlets/cords in the stand under the tank with the sump which places them in a "damp location" which can lead to excessive corrosion or water intrusion.. This is more than likely the problem.. Not a surge protector itself.
Its always a good idea to #1 include drip loops in all cords when the piece of equipment is located higher than the outlet and #2 don't put power strips in a damp location at all.


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 10/02/2012, 05:46 AM   #6
SaltyWenStirred
Registered Member
 
SaltyWenStirred's Avatar
 
Join Date: Jul 2012
Posts: 245
I also put a clear, outdoor, plastic outlet cover over my outlet to protect it from salt creep or saltwater.


__________________
Innovative Marine 38g Nuvo Tank; Skkye 92W LED light
Innovative Marine AuqaGadget - Skimmate Protein Skimmer, midsize
Innovative Marine MiniMax All-In-One Media Reactor (PhosGuard)

Nikon D90 35mm
SaltyWenStirred is offline   Reply With Quote
Unread 10/02/2012, 05:57 AM   #7
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
mcgyver, check into metal oxide varistors that heat up after excessive voltage spikes or long term use. there is a risk there. like you said, if used properly. which means you better be checking it for excess heat and replacing it often, but you cant pin a time frame, because how frequent are your voltage spikes. every system varies. thanks on the drip loop, forgot to mention that.
Quote:
Originally Posted by mcgyvr View Post
There is really nothing wrong with surge protectors or power strips when used properly.

Most of you like to "hide" your ugly outlets/cords in the stand under the tank with the sump which places them in a "damp location" which can lead to excessive corrosion or water intrusion.. This is more than likely the problem.. Not a surge protector itself.
Its always a good idea to #1 include drip loops in all cords when the piece of equipment is located higher than the outlet and #2 don't put power strips in a damp location at all.
willis, any of the online aquarium vendors carry them. marine depot etc.

Quote:
Originally Posted by lwillis22 View Post
So where can we get a grounding probe? I am not sure what these are.
nice.

Quote:
Originally Posted by SaltyWenStirred View Post
I also put a clear, outdoor, plastic outlet cover over my outlet to protect it from salt creep or saltwater.



__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill

Last edited by staindsoul; 10/02/2012 at 06:03 AM.
staindsoul is offline   Reply With Quote
Unread 10/02/2012, 06:22 AM   #8
jerpa
Registered Member
 
Join Date: Apr 2011
Location: Pittsburgh
Posts: 2,174
I wouldn't use half the surge protectors they sell on a lamp let alone my tank. The problem with most, besides the construction of the outlets themselves, is that they are contained in plastic boxes that melt, smolder, and sometimes burn when those components fail. Here is a good article on the various power strips available and the design flaws in many.

Outlet Strips

Quote:
Ground Probes

A ground probe should be used in your tank. It is used for stray voltages. (see bottom for stray voltages). A ground probe will put your tank at the same potential as your grounding conductor in your electrical system. IMO, you should use it with a gfci. The probe will put the tank at the same potential as your grounding conductor for tripping your circuit breaker. However during the time it takes to clear your breaker, your tank will be experiencing high current levels. If a gfci is used in conjunction with a ground probe, it will trip the circuit before the current reaches higher levels and may not even trip the circuit breaker.
I don't want to debate the necessity of the ground probe but I would argue that a GFCI MUST be used if a ground probe will be connected to the tank. I consider a GFCI mandatory anyway but using a ground probe without a GFCI introduces many potentially deadly scenarios that did not exist before.


__________________
Jer

Current Tank Info: 40b basement sump, 40b refugium, 30g frag

Last edited by jerpa; 10/02/2012 at 06:32 AM.
jerpa is offline   Reply With Quote
Unread 10/02/2012, 06:50 AM   #9
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
Quote:
Originally Posted by staindsoul View Post
mcgyver, check into metal oxide varistors that heat up after excessive voltage spikes or long term use.
MOV's were a serious problem YEARS ago (like in the 70's) because the epoxy used to encase them was highly flammable. Standards have changed quite a bit since then and now all MOV's used in surge strips are required to have a flammability rating of UL94V-0 or greater.


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 10/02/2012, 07:03 AM   #10
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
As to grounding probes..
First..yes you must use a GFCI outlet in combination with a ground probe..

The use of a ground probe is highly debated here.. Some (like myself) use one for my own personal protection and could care less if the increased potential to conduct current could be detrimental to the inhabitants of the tank.
Others don't use a ground probe simply because they feel this potential is damaging. But to date there is NO proof that a ground probe is bad for the tanks inhabitants and in fact there are cases that the introduction of a ground probe into a tank has cleared up head and lateral line disease in fish.

Pump motors,etc.. can create this "static stray voltage". If a ground probe is used that static voltage now has a path to ground and current "can" flow. But all I care about is that if the waterproof seal on my heater or pump or whatever decides to not do its job anymore that the ground probe will protect me when I place my hands into the tank.


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 10/02/2012, 09:47 AM   #11
knight2255
Registered Member
 
knight2255's Avatar
 
Join Date: Aug 2010
Posts: 313
Thanks, just picked up a ground probe.....didn't really understand the need until this thread.


knight2255 is offline   Reply With Quote
Unread 10/02/2012, 03:21 PM   #12
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
I agree with you and mcgyver, but I didnt want to command this and other items, because sure enough someone will come in and get all upset. Tried to stay nuetral, and just give my opinion. Not thou shalt.

Quote:
Originally Posted by jerpa View Post
I don't want to debate the necessity of the ground probe but I would argue that a GFCI MUST be used if a ground probe will be connected to the tank. I consider a GFCI mandatory anyway but using a ground probe without a GFCI introduces many potentially deadly scenarios that did not exist before.
Your welcome.

Quote:
Originally Posted by knight2255 View Post
Thanks, just picked up a ground probe.....didn't really understand the need until this thread.



__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill

Last edited by staindsoul; 10/02/2012 at 03:39 PM.
staindsoul is offline   Reply With Quote
Unread 10/02/2012, 10:01 PM   #13
sleepydoc
Registered Member
 
sleepydoc's Avatar
 
Join Date: Oct 2011
Location: Minneapolis, MN
Posts: 3,907
Still not clear on the need for a ground probe; assuming you have a GFCI, if there's a voltage capable of driving a current, the GFCI will trip, regardless of the presence or absence of a ground probe. (if you have a ground probe in the tank and current flows, it should trip as well.) If it is a voltage that can't drive a current, then there should be no concern.

I don't know the data on head/lateral line disease and grounding probes, so if it prevents it, that may be reason enough, regardless of theoretical safety issues.


__________________
~~~~~~~~~~~~~~~~~~~~~
120 gallon, coast to coast overflow w/beananimal overflow. Waveline DC 10000 II return pump, 40 gal sump, Octopus XS200 skimmer, T5 lighting
sleepydoc is offline   Reply With Quote
Unread 10/03/2012, 06:00 AM   #14
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
i believe that is the line where the debate starts about using a ground probe or not. the only scenario i dont like is, what if the gfi shunt trip has failure and wont trip. if i put my hand in there and i become the ground probe. not good. the ground probe would complete the circuit draw a high current and trip the breaker. it would harm the tank, but better them than me. this is thinking outside the ground probe putting the tank at the same potential as the grounding conductor and eliminating that potential voltage with no current. which in theory shouldnt be harmful to the inhabitants, but like mcgyvr said putting a probe in has cleared up some peoples issues.

i like it for my safety, as a backup to a gfi.

Quote:
Originally Posted by sleepydoc View Post
Still not clear on the need for a ground probe; assuming you have a GFCI, if there's a voltage capable of driving a current, the GFCI will trip, regardless of the presence or absence of a ground probe. (if you have a ground probe in the tank and current flows, it should trip as well.) If it is a voltage that can't drive a current, then there should be no concern.

I don't know the data on head/lateral line disease and grounding probes, so if it prevents it, that may be reason enough, regardless of theoretical safety issues.



__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill
staindsoul is offline   Reply With Quote
Unread 10/03/2012, 07:30 AM   #15
sleepydoc
Registered Member
 
sleepydoc's Avatar
 
Join Date: Oct 2011
Location: Minneapolis, MN
Posts: 3,907
Quote:
Originally Posted by staindsoul View Post
...but better them than me.
No disagreement on that point!

Quote:
Originally Posted by staindsoul View Post
like mcgyvr said putting a probe in has cleared up some peoples issues.
It'd be interesting to see if there's any data on that. I'm imagining not, but I'll have to see. Another possibility - it could be that the probe contributes trace amounts of titanium to the tank, or acts as some sort of scavenger and that clears up the disease, rather than the actual grounding itself. Absolutely no proof or data on that, but just a theory.


__________________
~~~~~~~~~~~~~~~~~~~~~
120 gallon, coast to coast overflow w/beananimal overflow. Waveline DC 10000 II return pump, 40 gal sump, Octopus XS200 skimmer, T5 lighting
sleepydoc is offline   Reply With Quote
Unread 10/04/2012, 03:20 PM   #16
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
Quote:
Originally Posted by sleepydoc View Post
It'd be interesting to see if there's any data on that. I'm imagining not, but I'll have to see. Another possibility - it could be that the probe contributes trace amounts of titanium to the tank, or acts as some sort of scavenger and that clears up the disease, rather than the actual grounding itself. Absolutely no proof or data on that, but just a theory.
like you said, i dont think there is any clear data. Mcgyvr mentioned it also. I would be inclined to think in those cases there was just enough of a current draw (in the low milliamps) that it affected the fish over time. my theory. Like the farmers that have stray voltage with cows being born with 5 legs and no butt.


__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill
staindsoul is offline   Reply With Quote
Unread 10/04/2012, 04:37 PM   #17
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
yeah there is no scientific data as the causes of HLLE is really still up in the air.. carbon/stray voltage,etc..

I have just read a few posts where HLLE issues went away after the introduction of a ground probe with no stated/known other changes.

I haven't seen a single post where a ground probe is proven to cause an issue though.


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 10/05/2012, 07:25 AM   #18
WillM
Registered Member
 
Join Date: Feb 2012
Location: Roanoke, VA
Posts: 663
I recently set up a tank and have had it running for about 2 months. I have tried putting some small soft coral as a sort of "canary in the coal mine". The zoas have fried looking skirts (looks like they get if you have an alk spike). All the parameters are normal otherwise (Nitrates are close to 0, alk 9, calcium 420, mag 1300).

The reason I'm posting here is that I can feel a small tingle when I place my hand in the tank, generally around cuts on my hands. This is not the way normal SW feels on my hands, I know what that is. This is definitely electrical. I don't have a voltmeter or any electrical know how beyond the basics. I unplugged everything and then started plugging it back in one at a time until I felt the tingle again. It is my lights, which aren't even immersed in the water (they are not the cheap crap aquatraders lights either, they are a little older, but made by coralife).

So, the question is, can the flourescent lights induce a current? My house is old so although the light fixture has a grounding prong, it isn't grounded. It's running on a timer that is not grounded. Grounding my house isn't really an option without rewiring everything and I just bought the house, so $3000 to rewire it isn't in the budget right now.

Then the follow up question, if I can feel this tingle, is that what is frying the zoas tips?


WillM is offline   Reply With Quote
Unread 10/05/2012, 07:37 AM   #19
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
how is your light mounted and how is everything plugged in (all one power strip, into one receptacle or gfi?)?

w/o a meter to actually see if have current flowing in the tank, this will be hard. i cant answer if the possible current is affecting the zoa tips, i havent personally seen the affect on corals.


__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill

Last edited by staindsoul; 10/05/2012 at 07:43 AM.
staindsoul is offline   Reply With Quote
Unread 10/05/2012, 07:44 AM   #20
Bike2k
Registered Member
 
Bike2k's Avatar
 
Join Date: Jul 2012
Location: Plantation, FL
Posts: 251
Can anyone recommend the b est way to install a ground probe?


__________________
Bike2k
Water parameters:PH: 8.0, SG:1.025, Ammonia:0, NO2:0, NO3:5, PO4:0.08,dKH:6.2,Ca :375,Mg:1080__75g DT, Solarmax H.O. (2) 54 watt T5 lights & night LEDs, RO NWB-150 skimmer, Eheim 1262 main pum
Bike2k is offline   Reply With Quote
Unread 10/05/2012, 07:52 AM   #21
WillM
Registered Member
 
Join Date: Feb 2012
Location: Roanoke, VA
Posts: 663
Quote:
Originally Posted by staindsoul View Post
how is your light mounted and how is everything plugged in (all one power strip, into one receptacle or gfi?)?

w/o a meter to actually see if have current flowing in the tank, this will be hard. i cant answer if the possible current is affecting the zoa tips, i havent personally seen the affect on corals.
The light is up on the standard mounting legs (3" above the rim of the tank). Everything is plugged into the one outlet, via a surge protected power strip. No GFCI protection, no grounding. I'm just wondering since it isn't grounded if buying another light is even going to fix the problem, but don't know enough about electricity to know if that even matters. I just don't want to blow money replacing the light and have the same exact problem when I plug in the new one. I guess I could try to get a light that doesn't need grounding, but it seems like most of my SW lights have the 3 prong plug in.

I'm pretty sure it has to be the electricity that is frying the zoas tips. The tank has been up long enough, the alk/cal/mag isn't out of whack, and there is a healthy chaeto population in the sump to zap the phosphates and nitrates.


WillM is offline   Reply With Quote
Unread 10/05/2012, 08:23 AM   #22
staindsoul
Calvin for President
 
staindsoul's Avatar
 
Join Date: Apr 2012
Location: R'VA
Posts: 509
^w/o a meter try this, plug that light fixture into a different power scource other than where the rest of the equipment is plugged in. see if that works.

im assuming all your receptacles are two prong in the house, and that is why your saying you dont have a grounding electrode. i would recommend get a gfi strip for the tank equipment. it will still work, you dont need the grounding prong for that too function. you will be alot safer.

you really need to check that fixture with a meter though.


__________________
Mitchell-60g, 2-A150W 10ks, 2-Hydor 425s, 1-240, 20gL sump/refugium

“Success consists of going from failure to failure without loss of enthusiasm” – Winston Churchill
staindsoul is offline   Reply With Quote
Unread 10/05/2012, 08:29 AM   #23
jerpa
Registered Member
 
Join Date: Apr 2011
Location: Pittsburgh
Posts: 2,174
Also don't assume your house isn't grounded just because it has two prong outlets. Many houses have a ground to the outlet box. They just didn't install 3-prong outlets.

Either way it would be worth hiring an electrician to install a GFCI outlet for the tank. It shouldn't set you back to much. The problem with the GFCI power strips is that they will trip if there is a power outage. An outlet doesn't trip so it will come back on with the rest of the house.


__________________
Jer

Current Tank Info: 40b basement sump, 40b refugium, 30g frag
jerpa is offline   Reply With Quote
Unread 10/05/2012, 08:41 AM   #24
WillM
Registered Member
 
Join Date: Feb 2012
Location: Roanoke, VA
Posts: 663
We just bought the house and had the home inspector go over it and it definitely doesn't have any grounding. It was built in 1957 and is a solid house, but the electrical wasn't redone since then I'm guessing.

I have a couple other issues that I'm going to have to get an electrician in there for, one of which is that the room that I have the tank in only has one outlet (ie the one I'm using for the tank), so I'll see what it would cost to GFCI up the outlets I use for my tanks while he is there to run more circuits to the rest of the house.

I've already got the ballpark price quote on getting the whole house grounded and replacing the outlets and that was more than I can drop at this stage in the game.

I'll run an extension cord in from the other room and see if plugging the light into another circuit stops the stray current in the tank.

I have a buddy that has a voltmeter, I'll see if he can come and test it for me.

Thanks for your your help and expertise


WillM is offline   Reply With Quote
Unread 10/05/2012, 08:51 AM   #25
Paul B
Premium Member
 
Paul B's Avatar
 
Join Date: Jun 2002
Location: Long Island NY
Posts: 15,549
I agree with everything the original poster said.
(Master electrician 40 years, Manhattan)


__________________
I used to get shocked when I put my hand in my tank. Then the electric eel went dead.

Current Tank Info: 100 gal reef set up in 1971
Paul B is offline   Reply With Quote
Reply

Tags
current, electrical, ground, stray, voltage


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 08:57 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.